You need to know the method of determining fire flow in your jurisdiction.
Once you know that, determine the fire flow and the number of hydrants req'd
to be used to get that flow.

 

Then, just simple hazen Williams formulae.  You will have starting flow and
pressure.  Plug and chug to prove it.

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Welch, Bobby
Sent: Tuesday, October 24, 2017 12:25 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Underground Main

 

I am working on a underground project were the new private fire main is
feeding the building sprinkler system and two hydrants. I am told that the
underground has to be calculated. I understand how I calculate the building
to prove that the sprinkler system will work but how do I prove that the
hydrants work as well?