Some of the fabric duct is designed not to collapse. I’m assuming this has been verified as not being that type?
Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 [email protected] From: Sprinklerforum [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Wednesday, November 08, 2017 5:06 PM To: [email protected] Cc: [email protected] Subject: Fabric Ductwork - ESFR obstruction? [EXTERNAL] NFPA 13, 07ed ESFR System What are the obstructions rules concerning a fabric supply duct installed below an ESFR system. The RTU will shut down and collapse the duct under any of the following conditions – Flow switch activation, heat detector and pull stations. I don’t think it should be considered an obstruction but we have a AHJ that is concerned that there could be up to a 60sec delay if the collapse is triggered by the flow switch and is requiring sprinklers below unless we can show otherwise. Thanks, Dewayne