Yes, it is the collapsible type.


*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *Prahl,
Craig/GVL
*Sent:* Wednesday, November 08, 2017 4:29 PM
*To:* [email protected]
*Subject:* RE: Fabric Ductwork - ESFR obstruction?



Some of the fabric duct is designed not to collapse.  I’m assuming this has
been verified as not being that type?




*Craig L. Prahl*
Fire Protection Group Lead/SME
*CH2M*
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected]



*From:* Sprinklerforum [
mailto:[email protected]
<[email protected]>] *On Behalf Of *Dewayne
Martinez
*Sent:* Wednesday, November 08, 2017 5:06 PM
*To:* [email protected]
*Cc:* [email protected]
*Subject:* Fabric Ductwork - ESFR obstruction? [EXTERNAL]



NFPA 13, 07ed



ESFR System

What are the obstructions rules concerning a fabric supply duct installed
below an ESFR system.

The RTU will shut down and collapse the duct under any of the following
conditions – Flow switch activation, heat detector and pull stations.

I don’t think it should be considered an obstruction but we have a AHJ that
is concerned that there could be up to a 60sec delay if the collapse is
triggered by the flow switch and is requiring sprinklers below unless we
can show otherwise.

Thanks,

Dewayne