That’s why I mentioned if he had a true 20x20. I couldn’t figure why you would 
want to do that with a 4.9k sprinkler. But I figured he had project specific 
reasons. 

I like how the 2016 edition cleared that up. I had many battles with AHJs about 
using the criteria in chap 8 for spray sprinklers to do room area / # of 
sprinklers In a room. 


Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Nov 21, 2017, at 8:14 AM, Pete Schwab <[email protected]> wrote:
> 
> Remember, if the room/compartment is 800 Sq Ft or less, you can average the 
> spacing of the residential sprinkler(s) over the room. It will not be 
> starting at 67 PSI.
>  
>  
> <image001.png>
>  
> Peter Schwab
> VP of Purchasing and Engineering technologies
>  
> Wayne Automatic Fire Sprinklers Inc.
> 222 Capitol Court
> Ocoee, Fl 34761
>  
> Mobile: (407) 468-8248
> Direct: (407) 877-5570
> Fax: (407) 656-8026
>  
> www.waynefire.com
>  
> <image002.jpg>
>  
> I sleep in a sprinklered home, do you?
>  
>  
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Travis Mack
> Sent: Tuesday, November 21, 2017 9:54 AM
> To: [email protected]
> Subject: Re: [EXTERNAL] Interesting issue .. residential sprinklers ..
>  
> If you are truly 20x20, then you are looking at 67 psi with the 4.9 vs 13 psi 
> with something like a Tyco EC-11. Do you have enough pressure where 50 psi is 
> of no issue?
> 
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook: 
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
>  
> Sent from my iPhone
> 
> On Nov 21, 2017, at 7:46 AM, John Irwin <[email protected]> wrote:
> 
> Yes. That’s an option as well. I have a pump so I am not terribly worried 
> about the demand. However the difference in price between a residential 
> pendent and something like a Tyco EC-5 is over $10. And I’m looking at over 
> 1,000 of these buggers.
>  
> John Irwin
> DynaFire Inc.
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Kyle.Montgomery
> Sent: Tuesday, November 21, 2017 9:44 AM
> To: [email protected]
> Subject: RE: [EXTERNAL] Interesting issue .. residential sprinklers ..
>  
> Residential sprinklers are “permitted” in dwelling units, not “required”, 
> right? Couldn’t you use any one of a number of commercial QR extended 
> coverage sprinklers?
>  
> That might mess you up if you are trying to do a 4-sprinklers residential 
> calc… or it could help because you could get a larger K-factor and lower 
> starting pressure for 20x20.
>  
> -Kyle M
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of John Irwin
> Sent: Tuesday, November 21, 2017 4:27 AM
> To: [email protected]
> Subject: [EXTERNAL] Interesting issue .. residential sprinklers ..
>  
> I am working on a project with a lot of 20x20 rooms in dwelling units. I have 
> a concrete deck so my piping will be exposed. I am trying to find a 20x20 
> solutions but keep running in to road blocks. Maybe someone has an idea.
>  
> The way I see it, I need one of the following …
>  
> I need a residential pendent sprinkler that can be installed with a deflector 
> distance from the deck greater than allowed by NFPA 13 OR I need a 
> residential UPRIGHT sprinkler listed for 20x20 spacing OR I need a listed 
> hanger attachment that will allow me to install 1" branch piping tight to a 
> concrete deck.
>  
> And go.
>  
>  
> John Irwin
> DynaFire, Inc.
>  
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to