Kyle:

Fire departments use radios to correspond with each other in real time, and 
they have the means to use their own equipment to tailor the water supply 
exactly to their needs as they work through a fire fight.   And keep in mind 
that they only want to use THEIR equipment to the greatest extent possible.   
Upon arrival, the first pumper in is going to connect to and charge the FDC.  
Connecting the interior attack lines to a manual standpipe entails first 
identifying the fire floor, then putting personnel into position to attack and 
selecting which hose connections will be used.  Most FDs attach a gate valve to 
the standpipe hose valve, then open the SP valve all the way to charge “their” 
valve – at that time they can bleed all the air until water hits the valve.  
Then they close their valve to take the SP valve (which was installed by who 
knows who and maintained by we don’t know) out of the equation.    Once their 
hoses are connected and they move forward on the attack, they’re connected to a 
water supply that they are confident CAN supply the pressure they need because 
their engineer is in charge of it and the SP system has been purged.

Steve Leyton



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kyle.Montgomery
Sent: Friday, December 08, 2017 7:00 AM
To: [email protected]
Subject: RE: [EXTERNAL] Re: Dry automatic standpipe without a pump

Yeah, but what good is it to connect to a water supply that can’t supply the 
pressure you need? The only thing that really makes sense is that they are 
doing it for supervisory purposes; i.e. someone breaks a pipe or opens a valve, 
water starts pouring out and an alarm sounds. But couldn’t you accomplish that 
(alarm part) with supervisory air only for a lot less money and without the 
potential for water damage?

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Gary Stites
Sent: Thursday, December 07, 2017 3:17 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] Re: Dry automatic standpipe without a pump

Item #3 says the source can be determined by the AHJ. Couldn't this arrangement 
(dry valve) be provided and then the water supply (pumper connection) be 
approved by said AHJ? Weird,but possible?

Gary Stites

On Tue, Dec 5, 2017 at 3:59 PM, Kyle.Montgomery 
<[email protected]<mailto:[email protected]>> wrote:
This actually does make a lot of sense. Maybe that is even what the City of 
Orlando intended when they wrote the code.

Couldn’t you just have supervisory air for that though, without actually being 
connected to a water supply with a dry pipe valve?

-Kyle M

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Taylor Schumacher
Sent: Tuesday, December 05, 2017 3:43 PM

To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] RE: Dry automatic standpipe without a pump

Definition/classification aside, I imagine the owner wants the connection to 
the water supply so as to monitor the integrity of the standpipe in case some 
brass bandit decided the hose valves had to be theirs or someone crashed into 
the piping and left it unusable.

-Taylor Schumacher

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ron Greenman
Sent: Tuesday, December 05, 2017 3:49 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Dry automatic standpipe without a pump

Doesn’t the addition requiring all Class I systems to have 2 ½” x 1 ½” reducers 
effectively turn it into a Class III? That is if I presume it to mean valves.

On Tue, Dec 5, 2017 at 1:33 PM Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:
How do you infer that?

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Kyle.Montgomery
Sent: Tuesday, December 05, 2017 1:29 PM

To: 
[email protected]<mailto:[email protected]>
Subject: RE: Dry automatic standpipe without a pump

That amendment seems to be poorly-worded as well. Do they allow Manual Wet 
standpipes in conditions that aren’t subject to freezing? Or do they prohibit 
all types of manual standpipes (wet or dry)?

Reading between the lines a little, it does look like Orlando requires 
AUTOMATIC standpipes, regardless, and thus Sean is dealing with a system that 
would already be out of compliance. Fun!

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Pete Schwab
Sent: Tuesday, December 05, 2017 2:06 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] RE: Dry automatic standpipe without a pump

All
This is located in the City of Orlando. Although I believe it would never 
freeze and if it did I would have to move to San Diego, Orlando has some very 
specific rules that really don’t make sense but they are there. It is based on 
the fact that we will have temperatures below 40 degrees which violates NFPA. 
They have a local fire code (Chapter 24). See 24.27. They require a dry valve. 
In addition they prohibit manual dry standpipes. So I call this an standpipe 
with an inadequate automatic supply. My opinion is wet would not freeze but 
this is an adopted ordinance so we follow it.
Pete








Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248<tel:(407)%20468-8248>
Direct: (407) 877-5570<tel:(407)%20877-5570>
Fax: (407) 656-8026<tel:(407)%20656-8026>

http://secure-web.cisco.com/1c_60jlhQXImGS0x8UN3GT53YFZhQ1WLy-LUp-Yr2mobn5JVTu_fkt-rhwwpp_JM7PlRmdLvVJ_jq1L5aA5bUDrdDxNevE6D8ALzDi6eZK1-0CVhw7v74h57HJCR5jIaFtaTqiEiLudwbt1ZWyvQxp0vYo_LA8jYOjc4IiMKwQDQcl00-7Ub2pDdhmoZ2_VGGSkskt5XVeg-JOwQoinVwBq4N0dz03DkF2iE52MM-L97waDu5RUA6GCpT0idcC_Ky/http%3A%2F%2Fhttp://secure-web.cisco.com/1Zzo9Q_BfMDjM_ikj9EuIkN1jSo_t-UWNLW_ABtvLOZ6y9s56U1VV1nIAmB3f9PFXKHlX9gREns_NFx7OxPZ0txc_zN12r0dn5ljrARhNUfGSMMvILdotWsFZYn20Pc7_rK1xOSSO5DrREqp__Sbr0cErjAd4MzsYaSU4s9uS49ewg9Xxh6PW9VKrb41SEYMhk8tjTUi3g2bI3fZbb5vZfDKvBKsy0jR5DKenuNSNTstgbfsw7oB7wY5Nr5TTxm6Uue0m2plPEDZYMxNHVbQxpA/http%3A%2F%2Fwww.waynefire.com<http://secure-web.cisco.com/1xdYrvXLkNDQOZvNvpmzAcxE008RGeIyJJvrNLi59lYkg_rkehOQHlhgjescS7gK-7sPu6_XI7Js0EWg682gaC092nkE7u-pNz5-a2id8eQEpV8dQcZkz06BU3PgSprAZfHC-vdl36HOHlXNFn3gPzwsGOzMgggsayASUw4BeQpQIouNqpIbR0KLbXUCzimXLFeLNXwu-HtsLYUBSubBGXpTsZksMNUUhPB76Lf2C9O4QHTAAM-xE9yf2_De9PAgv/http%3A%2F%2Fwww.waynefire.com%2F>



I sleep in a sprinklered home, do you?



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of MFP Design, LLC
Sent: Tuesday, December 05, 2017 2:31 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Dry automatic standpipe without a pump

Definitely don’t let the past description or even system get in the way.  It is 
what it is.  If the original is wrong, the owner can go back and fix it.  But 
there is no reason to continue an error just because it was done that way in 
the past.  Those are the most dangerous words in this industry: “We always did 
it that way!”

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Tuesday, December 5, 2017 12:26 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Dry automatic standpipe without a pump

If you let that issue become your issue, then yes that’s the issue.   If the 
“other contractor” has erroneously or deficiently described or left the work in 
place and the owner is relying on that, it should be an issue between those 
parties and not you.

In other words, what is an “issue”?

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Sean Lockyer
Sent: Tuesday, December 05, 2017 11:09 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Dry automatic standpipe without a pump

Understood Steve; however, when I say “a pump is needed” I am assuming that is 
because they would not be allowed to use the pumper on the fire truck. However, 
if this turns out to be, by definition, a manual standpipe then we would be 
able to use the pumper and as a result, this issue would most likely go away.

I guess the issue here is what the original contractor defined as an automatic 
and what they defined as a manual. In other words, what is “is”.


              Sean Lockyer
              Project Designer                               4617 Parkbreeze 
Court
              Cell    386-279-1197<tel:(386)%20279-1197>                        
      Orlando, Florida 32808
              [email protected]<mailto:[email protected]>     
         Phone:      407-816-9101<tel:(407)%20816-9101>
              
http://secure-web.cisco.com/1_bUqSQn0X2ItLZjhiK8VC8_d8cPrOYY_Syyc_8cgSS_JYmSSLkZCoJWuJaUQKBTlo3Jf9eXx6c-0dtUfN1ztxYKqzAIGGCvhBjigRFEWsXNoeLVNy3X-rFo1m2Wv1r9hWnachg_uPARPKJ2n-8RlznCUFaaXU8MR5AovCZ5CGc7spy4QYQ19sK0o9mcx1xSKkuxvuRCJ_--IMoZK99MDUQmP4mahHTZasXIuQi_Ua1OukHPgHJcTmsA_ix4tPfCK/http%3A%2F%2Fwww.AITLifeSafety.com<http://secure-web.cisco.com/1ehR6VvsmdXfQf4zfvzFFlsdMQ3jUpOskpwTyyEuzgA6O_M4o4_9BaiduVexsVpLyiChX8i6JJuzCIg9DkCA5qGMi3XbFyLgoeIlx-_aVqluzomLbVs-9_POCDHksA2ykLmZrf74yv9W7eZ13uCD5LQ8G-nZ6nOfhAJe-FunppMZVrOtzo5wR2HEAcZY-WtbaY9SsPiMh-Ws7DjSFG6qnaCu1HKUPN20l79By9QNnJ2Vp6tDcjnQruM7sYYDI49We/http%3A%2F%2Fwww.aitlifesafety.com%2F>
                       Fax:         407-816-9104<tel:(407)%20816-9104>


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://secure-web.cisco.com/1F_3sEzFxihrq46DFt-IuMlEvBjOoktHpegLC-Lv6JzieCRPrlG_CYTZPjSt1AOy1eQKOyca07zBM_JyUOfHZzTT5b9IPQNx-KfUay78EcK6PvBUUKhtArx7kAtfUFvdUrI6YdJnVkspgnVYVydsmitjZm-0sRCAkMqusdMV16fS5VxlPvJAHVU9sPofeC28asqCLAcC5n-VbQBpuxGeMpE_2HsAqL33KZu8v1j8XUDzBm0yDf7OQB-drKF9yAHb9McpMI2cCL9F3e9FMDnF97w/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org
--
Sent from Gmail Mobile

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://secure-web.cisco.com/1uKC_u7Kkp0peih_YgVQ5edNs5g0FpmF0Hry1N8i8xl8gO5cBM5wqbgnA5UEYRnAruVJSkaXGMXepWtM3cjwel6-A_F2hbbzmmftxFYkECwBKsWZxjR5uf5hSLHR9JJxi7N0VVdpIE2pcAMuNvn0mpCCvwDX_0dXMuoqqb1ar6qOzfUSLWXYYDy6gxiM8aS4CqicDVvf1T7FI8FlGm1kEAI-45zZrYPIleSF0Hnenr_k2FwmUKB0sA71lOtLranQmKWaSUG_gpjSUs_wa3oAMhw/http%3A%2F%2Flists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<http://secure-web.cisco.com/1-ehJskrQWvspn_VLQHDARQxMuiRouclx7B9XxGHtGuAeXWg3doUKXZiM7XFFn_VdPnUWORhUV6G2HIrWeTQXNfSvi7BL8Ii8uWEfhHG9Db-eAnt-OBmaCX1MhRoC9fs-wftur0fIx4FToZqt7e5oBGdDec4nG6aZniGMopMWkxLoFrrfxSX85feXRFaZ79A8SCWJt_8HA_7N3ItcA9CsGS8er9QELnB6bgNqo8dcrq57p70nQzzp9VPMQu41TsmpQvG9pjvkMAGlyXlXOjq9Bg/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org>



--
Gary Stites
805-769-GMAN

RLH<http://secure-web.cisco.com/18birFvs_uUAf68xccFG6xQttZYJTPQWKt1bc-md0t_JUJn60U2L4RoVQClZKwEg2tXG9B8lZwJDOy7Mf6qovwZvjdzc-48pjKgpcvPuC3wI20CtT8oOsSuh7K4-_kzOuHClXTYYi3s0oBmAjRrUac9alRc3RPyYUtPDT0WfOloLRV4SS1B3RwuEpmU4q5d-FpOIZABbywAqp7nAvGgzDtkvO2uUtle2b5jTEAsp9dUt5_4iPbD1Sw-N64J34SjdSKlceksxeGJjUW0r1M5yPDg/http%3A%2F%2Fwww.rlhfp.com>
http://secure-web.cisco.com/15R3ndoMzy8s6LhWLEc8XRGOvEK63bd5e-bWFy6oxlCPVjZprThtstc_e2OZ0ahrKw2t1dD9UVVDW5Zx6HDsGNk-bSnPxnJ0n3JrX6C7Gyy5yQA6H0c9WKVCCcExsB-nzz9MYp235fm_uGE0G5SapWplnuL-lEAdMrPgFxh5rk6BhS8xTOeqb8PRwB-9FYJZCSb16uxDzpbVG6tGOvqctqy4xMw7tgpZjdzG6As8Abl4GaIZhYLXIUVyal66UALabP52NdLZM9bX5rDI3lCxUig/http%3A%2F%2FWWW.K25.Rocks
Pandora Station<http://www.pandora.com/?sc=sh43464983213902734>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to