Normally if they are movable, you just provide protection in the closed "pocket"

Fixed is another ball game.

R/
Matt

Matthew J. Willis
Design Manager /3-D Specialist
Rapid Fire Protection Inc.<http://rapidfireinc.com/>
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108

[cid:[email protected]]



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Larrimer, Peter A
Sent: Tuesday, December 12, 2017 6:56 AM
To: [email protected]
Subject: Protection under bleachers in a Gymnasium

I was doing some research and found this "Ask the AHJ" statement in the 2016 
Sprinkler Handbook.

Should an authority having jurisdiction reject or comment on a proposed fire 
sprinkler system for a
gymnasium where there is no fire sprinkler protection shown under the bleachers?

Yes. Although bleachers are typically moveable, they are a permanent part of 
the space and need to
have protection underneath per 8.5.5.3.1 where they are more than 4 ft (1.2 m) 
wide from the wall when
extended. This is similar in nature to an overhead door obstruction mentioned 
in this section.

My question is how do you properly provide sprinkler protection under a set of 
moveable bleachers?

Thanks

Peter A. Larrimer, P.E.
Fire Protection Operations Manager
Office of Occupational Safety, Health, and GEMS Programs (10NA8)
Veterans Health Administration
Department of Veterans Affairs
Office/Mobile: (412) 999-1321