According to NFPA you can do a 13-R for the first four floors and a 13 system on the 5th floor and attic. I think you need to look at the IBC/IRC to see if there are building code requirements in the crawl space (assuming a normal crawl space).
Duane T. Fox, Jr., CFPS, CFI, CFPE Asst Chief, Technical Services DE State Fire Marshal's Office 302-856-5298 From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Thursday, January 11, 2018 2:30 PM To: [email protected] Subject: Apartment Crawl Space Looking at a (5) story apartment building so I assume it would need to be per NFPA-13 correct? With that being said is there anything in the Standard that addresses the crawl space underneath? Concealed Space? Brian Harris, CET BVS Systems Inc. Design Manager bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935