Guys:

I have been pouring over 13 all afternoon and I can't find the requirement for 
the scenario I am dealing with, so I humbly ask for your help.

                Hazard: Diesel Engine Mfg plant                 - Loading dock 
area

-          30' Deck, 20' Mics Rack Storage, Grp A Plastic containers with metal 
parts.

                Existing System(s)                           8"x2.5"X8" Grid
                                                                                
K 8.0 Uprights
.60 GPM/4,000 sq. ft.

The insurance carrier has done a loss prevention survey and their written 
report says they will accept the omission of in rack sprinklers if the overhead 
system will support K-16.8 heads and a design density of
.80 GPM/2,000 sq. ft. under section 17.2.1.2.1 (e)  (which it will with a large 
safety factor)

My question is this:         What restrictions do I have with the overhead 
sprinklers and mixing the sprinkler K factors?
Do all of the heads on the system need to be changed to K16.8 or just the ones 
within 40' of the racks?
                                                If I can mix K factors, do I 
need a 2' draft curtain in between like I would if it were ESFR?


Thanks,