I love this. Two responses 180 degrees out. I think I described why I’d go
with the sprinkler listing. Nick, why do think the element type supersedes
the sprinkler listing?

On Thu, Feb 15, 2018 at 3:04 PM Ron Greenman <[email protected]> wrote:

> The confusion is as is often the case the words. That standard response
> being used for both element and sprinkler listing creates an equivalency in
> ones head. I’d argue that the fast response element is often found in
> sprinklers listed as standard resonate but a standard response element is
> never found in a quick response sprinkler. I’d argue the listing of the
> sprinkler in the application is driver and that you have a compartment in
> which all the sprinklers need to be standard response per the rules of
> their listing(s).
>
> On Thu, Feb 15, 2018 at 2:28 PM Ed Kramer <[email protected]> wrote:
>
>> Reference section 8.3.3.2 of the 2013 edition of NFPA 13:  “Where QR
>> sprinklers are installed, all sprinklers within a compartment shall be
>> quick-response unless otherwise permitted in 8.3.3.3.”  Section 8.3.3.3
>> isn’t applicable for this question.
>>
>>
>>
>> I’m protecting an OH II sales area with EC sprinklers spaced (mostly) at
>> 18’x18’.  This particular sprinkler is listed as SR at that spacing, but is
>> listed as QR for 14’x14’ and smaller spacing.  This sales area has a small
>> 20 sf nook (not a separate compartment) that requires an additional
>> sprinkler.  My intent is to protect that nook with a K5.6 sprinkler.
>>
>>
>>
>> Should the K5.6 sprinkler be SR or QR?
>>
>>
>>
>> The answer is probably SR since the EC sprinklers are installed at a
>> spacing that has a SR listing.  But that would be mixing a
>> standard-response element with a fast-response element – something I’ve
>> been led to believe is not cool.
>>
>>
>>
>> The 2016 flavor of NFPA 13 has a new section 8.3.3.5 that allows mixing a
>> SR listing with a QR listing as long as it’s the same sprinkler (and
>> therefor both have the same fast-response element).
>>
>>
>>
>> Anybody want to give their 2 cents?
>>
>>
>>
>> *Ed Kramer*
>>
>> Bamford Fire Sprinkler Co., Inc.
>>
>> 5134 Merriam Dr./Shawnee Mission, KS  66203
>>
>> Phone: 913-432-6688  Fax: 913-432-5294  Cell: 785-766-4894
>>
>> [email protected]
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
> --
> Sent from Gmail Mobile
>
-- 
Sent from Gmail Mobile
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to