Look at what the 2016 has added. My first read is the bulb type is what is 
important.  But let me state, I’m not looking at the book and going from 
memory. My personal opinion is the QR would be a better choice but I need to do 
some research before commit 100%.

John August Denhardt, P.E.
Strickland Fire Protection

On Feb 15, 2018, at 6:43 PM, Ron Greenman 
<[email protected]<mailto:[email protected]>> wrote:

John, you can’t mix them. So is it the bulb size I can’t mix or the listing in 
the application? What if it’s a fast response link in a typically QR sprinkler 
that is listed SR in this application? I think your reasoning and Nick’s and 
mine all have merit, but I think we’re trying to parse out what this all means 
in 13. I’m just reading the rules without concern for which is best in an 
actual situation because then you gave to ask which works first and then if 
more than one goes which is best. I don’t think the code can tell us that.

On Thu, Feb 15, 2018 at 3:28 PM John Denhardt 
<[email protected]<mailto:[email protected]>> wrote:
My 3 cents.  I would us the QR.  The other sprinklers are QR but in this 
application, they only receive the SR.

QR provides better protection in my opinion.

John

John August Denhardt, P.E.
Strickland Fire Protection

On Feb 15, 2018, at 5:28 PM, Ed Kramer 
<[email protected]<mailto:[email protected]>> wrote:

Reference section 8.3.3.2 of the 2013 edition of NFPA 13:  “Where QR sprinklers 
are installed, all sprinklers within a compartment shall be quick-response 
unless otherwise permitted in 8.3.3.3.”  Section 8.3.3.3 isn’t applicable for 
this question.

I’m protecting an OH II sales area with EC sprinklers spaced (mostly) at 
18’x18’.  This particular sprinkler is listed as SR at that spacing, but is 
listed as QR for 14’x14’ and smaller spacing.  This sales area has a small 20 
sf nook (not a separate compartment) that requires an additional sprinkler.  My 
intent is to protect that nook with a K5.6 sprinkler.

Should the K5.6 sprinkler be SR or QR?

The answer is probably SR since the EC sprinklers are installed at a spacing 
that has a SR listing.  But that would be mixing a standard-response element 
with a fast-response element – something I’ve been led to believe is not cool.

The 2016 flavor of NFPA 13 has a new section 8.3.3.5 that allows mixing a SR 
listing with a QR listing as long as it’s the same sprinkler (and therefor both 
have the same fast-response element).

Anybody want to give their 2 cents?

Ed Kramer
Bamford Fire Sprinkler Co., Inc.
5134 Merriam Dr./Shawnee Mission, KS  66203
Phone: 913-432-6688  Fax: 913-432-5294  Cell: 785-766-4894
[email protected]<mailto:[email protected]>

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--
Sent from Gmail Mobile
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to