I believe that means a HE foam system plus a sprinkler system with a .30 density.
Art Tiroly ATCO Fire Protection 24400 Highland Rd CLE 44143 216-621-8899 216-570-7030 cell -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Tony Silva Sent: Friday, February 23, 2018 3:39 PM To: [email protected] Subject: Tire Storage NFPA 13, 2014 Table 18.4(a) Some "Sprinkler Discharge Densities" are given as (for example): "0.30 plus high expansion foam" Does this mean the roof system needs to be high expansion foam with a density of 0.3? I'm just confused with the use of the word "plus" and want to make sure it doesn't mean anything else. Thanks, Tony -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org /attachments/20180223/131521aa/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org --- This email has been checked for viruses by Avast antivirus software. https://www.avast.com/antivirus _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org