Mike, NFPA 13 (2016) A-8.1 "... no sprinkler piping should be placed in an unsprinklered area unless the area is permitted to be unsprinklered by this standard." If sprinklers are allowed to be omitted per 8.15.6 then there should not be a problem with the piping in the crawl space.
-----Original Message----- From: Sprinklerforum <[email protected]> On Behalf Of Michael Hill Sent: Tuesday, March 13, 2018 1:39 PM To: [email protected] Subject: Sprinkler Pipe Passing Thru Unsprinklered Areas I seem to remember being told early on in my fire protection career that sprinkler pipe could not pass thru unsprinklered areas of an otherwise sprinklered building. Does anyone know where this comes from or if it is even a requirement? In my case the water comes from the BFP passes thru an unconditioned (different problem that I know how to handle) and unsprinklered crawl space to a fire pump. Water goes from the fire pump passes back thru the same crawl space to a standpipe with floor control assemblies. Water from the floor control assembly then goes back thru the same crawl space to the occupied portion of the building where the fire pump is. This was someone else's design that the GC wants me to follow. I am looking for arguments for why this isn't the best way to run these pipes. Common sense does not apply here. Mike Hill _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org -------------- next part -------------- A non-text attachment was scrubbed... Name: Dale Wingard SET.vcf Type: text/x-vcard Size: 26062 bytes Desc: Dale Wingard SET.vcf URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180313/9eb3cb9c/attachment.vcf> _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org