Unless your state has amended IBC, it says what it says in 905.3.4.
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of Fpdcdesign
Sent: Thursday, March 15, 2018 1:09 PM
To: Sprinklerforum
Subject: Re: stages
I haven’t run into a situation where we have been allowed to tap off a
sprinkler system. All of then ones I have seen require a new feed from the
riser and a full standpipe calc.
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)
>
> On Mar 15, 2018 at 3:57 PM, <Steve Leyton
> (mailto:[email protected])> wrote:
>
>
>
> What Reed said - it can be either a small hose connection or a standpipe. I
> think small hose connection is the simplest classification and you add 50 GPM
> to the POC (or to each of two depending on size/configuration of the stage).
> It might also be worth a chat with the responding FD to see if you can get
> relief from the installation of hose and nozzle. What we've done in the past
> for some FDs is furnish a 2½" FHV with a 2½" x 1½" reducer and no hose. If
> the FD ever needed more water out of the valve they could pump the FDC like
> crazy.
>
> Highly unlikely these connections will ever be used in a real-world scenario
> regardless of how they're configured but the code says what it says ...
>
> The preceding is my personal opinion only, Steve Leyton
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of
> Reed A. Roisum, SET
> Sent: Thursday, March 15, 2018 12:46 PM
> To: [email protected]
> Subject: RE: stages
>
> You can come off the overhead system with a 1 ½" hose connection in a fully
> sprinklered building. Here is a reference from 2009 IBC regarding stage hose
> connections... note the exception. I think it is the same in the more current
> codes, just had this one handy.
>
>
>
> [F] 905.3.4 Stages. Stages greater than 1,000 square feet in area shall be
> equipped with a Class III wet standpipe system with 1 1/2-inch and 2 1/2-inch
> hose connections on each side of the stage.
>
>
>
> Exception: Where the building or area is equipped throughout with an
> automatic sprinkler system, a 1 1/2-inch hose connection shall be installed
> in accordance with NFPA 13 or in accordance with NFPA 14 for Class II or III
> standpipes.
>
>
>
> [F] 905.3.4.1 Hose and cabinet. The 1 1/2-inch hose connections shall be
> equipped with sufficient lengths of 1 1/2-inch hose to provide fire
> protection for the stage area. Hose connections shall be equipped with an
> approved adjustable fog nozzle and be mounted in a cabinet or on a rack.
>
>
>
> I have found that many fire departments do not want these installed so worth
> checking...actually, State of MN amended out this section in their building
> code.
>
>
>
>
>
> Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection
> Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 |
> KFIengineers.com<http://www.kfiengineers.com>
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of
> MFP Design, LLC
> Sent: Thursday, March 15, 2018 2:24 PM
> To: [email protected]
> Subject: stages
>
>
>
> I need to confirm something before I go over the deep end. Well, maybe I
> already have.
>
>
>
>
>
> With regard to the hose valves at the side of a true stage, are these to be
> treated as a standpipe where you need 250 gpm @ 100 psi provided through the
> FDC and routed on a separate system? Or can you come off the overhead system
> and just add 50 gpm per hose valve for your inside hose requirements?
>
>
>
>
>
>
>
>
>
> Travis Mack, SET
>
>
>
> MFP Design, LLC
>
>
>
> 3356 E Vallejo Ct
>
>
>
> Gilbert, AZ 85298
>
>
>
> 480-505-9271
>
>
>
> fax: 866-430-6107
>
>
>
> <mailto:email:[email protected]> email:[email protected]
>
>
>
>
>
> <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi
>
> gn.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da4
>
> 2e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2
>
> FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0> http://www.mfpdesign.com
>
>
>
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebo
>
> ok.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b
>
> 4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C6363790166
>
> 77342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
>
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>
>
>
> Send large files to us via:
>
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta
>
> il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C
>
> 14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2
>
> wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
>
> https://www.hightail.com/u/MFPDesign
>
>
>
> LinkedIn:
>
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked
>
> in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%
>
> 7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L
>
> sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
>
> https://www.linkedin.com/in/travismack
>
>
>
>
>
> "The bitterness of poor quality remains long after the sweetness of low price
> is forgotten."
>
>
>
>
>
> -------------- next part --------------
>
> An HTML attachment was scrubbed...
>
> URL:
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/4ed72f10/attachment.html>
>
>
> -------------- next part --------------
>
> A non-text attachment was scrubbed...
>
> Name: image001.jpg
>
> Type: image/jpeg
>
> Size: 6420 bytes
>
> Desc: not available
>
> URL:
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/4ed72f10/attachment.jpg>
>
>
> _______________________________________________
>
> Sprinklerforum mailing list
>
> [email protected]<mailto:[email protected]>
>
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
> ______________________________________________________________________
>
> This email has been scanned by the Symantec Email Security.cloud service.
>
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/adfca750/attachment.html>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/cfb7b1ed/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org