I have an existing hospital where they are building a new 4 story addition
that will require manual-wet standpipes.  The problem arises is that we are
using an existing common feed riser which has a control valve on it in the
fire pump room.  I know this violates section 6.4.1 (NFPA 14 – 2010ed)  for
no control valves between the FDC and standpipe system.  Is there anything
the precludes me from installing an additional FDC on the new addition to
use the existing feed and satisfy 6.4.1?