I would say this situation would be covered by NFPA 13 2016 8.17.2.4.5,
which is also referenced in Table A.6.9 in NFPA 14 2016.


------------------------------


*Mike Morey*
*CFPS 3229 • NICET S.E.T. 123677*
*Project Manager* • Fire Protection Group
*Shambaugh & Son, LP **an EMCOR Company*
7614 Opportunity Drive • Fort Wayne, IN • 46825
*direct *260.487.7824* /  cell *260.417.0625* /  fax *260.487.7991
*email *[email protected]







From:        Dewayne Martinez <[email protected]>
To:        [email protected]
Cc:        Dewayne Martinez <[email protected]>
Date:        04/03/2018 07:13 AM
Subject:        Remote additional FDC
Sent by:        "Sprinklerforum" <
[email protected]>
------------------------------




BE ADVISED - This email originated outside EMCOR.


I have an existing hospital where they are building a new 4 story addition
that will require manual-wet standpipes.  The problem arises is that we are
using an existing common feed riser which has a control valve on it in the
fire pump room.  I know this violates section 6.4.1 (NFPA 14 – 2010ed)  for
no control valves between the FDC and standpipe system.  Is there anything
the precludes me from installing an additional FDC on the new addition to
use the existing feed and satisfy 6.4.1?
Thank you,

Dewayne Martinez
Fire Protection Design Manager

*TOTAL* *Mechanical*
*Building* *Integrity*

W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.total-2Dmechanical.com_&d=DwMFaQ&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=ZOxRRaZgf_AM3xCvRTnuDxTRxPttJJdJxk2c4fexLYA&s=yavv4Zee55Ow3pDpBxztkUy-WA9Ay3v-uSGu-K-gX7Q&e=>

[image: Consecutive Honors 2012-2017]
 _______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=ZOxRRaZgf_AM3xCvRTnuDxTRxPttJJdJxk2c4fexLYA&s=J_oppKbRPdkBZJc4SXO1kTyit03JWUIDIs4wVB8c75o&e=

This message is for the named person's use only. It may contain
confidential, proprietary or legally privileged information. No
confidentiality or privilege is waived or lost by any mistransmission. If
you receive this message in error, please immediately delete it and all
copies of it from your system, destroy any hard copies of it and notify the
sender. You must not, directly or indirectly, use, disclose, distribute,
print, or copy any part of this message if you are not the intended
recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to