What software package is it?

Matt



From: Sprinklerforum <[email protected]> On Behalf 
Of Dewayne Martinez
Sent: Tuesday, April 17, 2018 7:39 AM
To: [email protected]
Cc: Dewayne Martinez <[email protected]>
Subject: RE: Supply calculation for manual-wet standpipe

I am not used to seeing this calc program so I may be looking at this wrong but 
I don’t see a water supply on this graph.
[cid:[email protected]]

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]<mailto:[email protected]>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
[Consecutive Honors 2012-2017]

From: Dewayne Martinez 
<[email protected]<mailto:[email protected]>>
Sent: Tuesday, April 17, 2018 6:42 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Dewayne Martinez 
<[email protected]<mailto:[email protected]>>
Subject: RE: Supply calculation for manual-wet standpipe

I initially put in a supply of 150psi at 1000gpm and then modify it until I get 
a 0 PSI cushion.

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]<mailto:[email protected]>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
[Consecutive Honors 2012-2017]

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Matt Grise
Sent: Tuesday, April 17, 2018 6:26 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Supply calculation for manual-wet standpipe

When you say that  you tweak it to find the actual demand – does your software 
not tell you the psi input required to supply the hose demand you request at 
the standpipe outlets? I usually see ‘required pressure’ as an output of the 
software no matter what the input is.

Matt


From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Dewayne Martinez
Sent: Tuesday, April 17, 2018 6:02 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Dewayne Martinez 
<[email protected]<mailto:[email protected]>>
Subject: Supply calculation for manual-wet standpipe

One of my free lancers sent me a supply calculation for a manual wet standpipe. 
 I have always put in a “pumper connection” supply at the FDC, did a demand 
calc and tweaked it until I ended up with a zero pound cushion to see what was 
really required.  His way looks to be good.  Have I been taking the hard way 
around to solve what PSI is required at the FDC?
Thanks,

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]<mailto:[email protected]>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
[Consecutive Honors 2012-2017]