If there was ever a situation in which a good old-fashioned hand calc’ was the 
best and easiest solution …   You can literally use the simplified method from 
13D y’all …

The foregoing is my opinion only and is not intended to represent the NFPA 14 
Technical Committee, nor serve as an interpretation of the standard.

Steve Leyton
Protection Design & Consulting
San Diego, CA




SML

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Fire Design
Sent: Tuesday, April 17, 2018 9:22 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Supply calculation for manual-wet standpipe

I use hydracalc and it looks like what the designer did was just do a standard 
supply&demand calc but did not enter water supply information - which you can 
do. When done this way the calculations output the graph you show but does not 
include the supply since it was not entered. I guess he's leaving it up to you 
or the reviewing authority to determine if they can meet the demand with their 
pumper trucks.


[https://ipmcdn.avast.com/images/icons/icon-envelope-tick-round-orange-animated-no-repeat-v1.gif]<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>

Virus-free. 
www.avast.com<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>


On Tue, Apr 17, 2018 at 7:41 AM, Steve Leyton 
<st...@protectiondesign.com<mailto:st...@protectiondesign.com>> wrote:
Danger!   Don’t assume standard practices, get the inlet pressure from the 
serving FD and reference that agency as the source of the “Flow Test Data”.

The foregoing is my opinion only and is not intended to represent the NFPA 14 
Technical Committee, nor serve as an interpretation of the standard.

Steve Leyton
Protection Design & Consulting
San Diego, CA




Steve

From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of Mike Stossel
Sent: Tuesday, April 17, 2018 6:44 AM

To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Supply calculation for manual-wet standpipe

I believe to be certified under the guidelines of NFPA 1901 the minimum the 
pumper would supply is 150psi @1,000gpm, 200psi @ 750gpm and 250psi @ 500gpm.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack
Sent: Tuesday, April 17, 2018 9:41 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Supply calculation for manual-wet standpipe

Demand was only 750. Typically pumper truck will deliver more psi at only 750 
gpm.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Apr 17, 2018, at 6:35 AM, Rocci 3 Cetani 
<roc...@norcalfire.com<mailto:roc...@norcalfire.com>> wrote:
Looks like hydra cad and also looks like he is over the standard pumper trucks  
150 PSI…..unless your pumper trucks pump more than 150 PSI I would have him 
look at it again

Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III

Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590


roc...@norcalfire.com<mailto:roc...@norcalfire.com>
www.norcalfire.com<http://www.norcalfire.com/>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information
belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Matt Grise
Sent: Tuesday, April 17, 2018 6:20 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Supply calculation for manual-wet standpipe

What software package is it?

Matt



From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Dewayne Martinez
Sent: Tuesday, April 17, 2018 7:39 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Dewayne Martinez 
<dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>>
Subject: RE: Supply calculation for manual-wet standpipe

I am not used to seeing this calc program so I may be looking at this wrong but 
I don’t see a water supply on this graph.
<image001.png>

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
<image002.jpg>

From: Dewayne Martinez 
<dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>>
Sent: Tuesday, April 17, 2018 6:42 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Dewayne Martinez 
<dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>>
Subject: RE: Supply calculation for manual-wet standpipe

I initially put in a supply of 150psi at 1000gpm and then modify it until I get 
a 0 PSI cushion.

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
<image002.jpg>

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Matt Grise
Sent: Tuesday, April 17, 2018 6:26 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Supply calculation for manual-wet standpipe

When you say that  you tweak it to find the actual demand – does your software 
not tell you the psi input required to supply the hose demand you request at 
the standpipe outlets? I usually see ‘required pressure’ as an output of the 
software no matter what the input is.

Matt


From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Dewayne Martinez
Sent: Tuesday, April 17, 2018 6:02 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Dewayne Martinez 
<dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>>
Subject: Supply calculation for manual-wet standpipe

One of my free lancers sent me a supply calculation for a manual wet standpipe. 
 I have always put in a “pumper connection” supply at the FDC, did a demand 
calc and tweaked it until I ended up with a zero pound cushion to see what was 
really required.  His way looks to be good.  Have I been taking the hard way 
around to solve what PSI is required at the FDC?
Thanks,

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
<image002.jpg>

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to