All true, but apples to oranges. A commercial woodshop is a step above a school 
woodshop. We do an awful lot of schools work and you would be amazed at what a 
modern high school woodshop looks like Mark. Multi station dust collectors are 
the norm. It's definitely at least an ordinary hazard. A commercial wood shop 
is  Extra Hazard, the debate there being whether it's Group 1 or Group 2.



Sent from my Verizon, Samsung Galaxy smartphone


-------- Original message --------
From: "Mark.Phelps" <[email protected]>
Date: 4/21/18 2:15 PM (GMT-08:00)
To: [email protected]
Subject: Re: [EXTERNAL] Re: Wood Shop Classroom Classification of Hazard

The one thing I would add to this is to compare the fire loading between a 
commercial cabinet/wood shop and the classroom environment. A typical 
commercial shop would have sheet goods and lumber inventory for hundreds of 
cabinets, as well as hundreds of boxed finished goods. A typical wood shop 
classroom environment would have nothing close to that.

Mark at Aero
602 820-7894

Sent from my iPhone

On Apr 21, 2018, at 3:34 PM, Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:

NFPA 13 speaks to the nature of the use, not just the label of a particular 
building or compartment. If it has fire load, or processes, or byproduct of 
those processes that make it more hazardous, then it's more hazardous. Out here 
in California were used to fire protecting vocational technology and science 
and shop (auto, wood, metal) classrooms to the higher hazard classification 
because they may contain pressurized natural gas, welding or soldering, 
flammable liquids, open burners higher levels of dust, etc.

I agree with you - stay the course.

Steve L.


Sent from my Verizon, Samsung Galaxy smartphone


-------- Original message --------
From: joseph kuerzi <[email protected]<mailto:[email protected]>>
Date: 4/21/18 11:42 AM (GMT-08:00)
To: 
[email protected]<mailto:[email protected]>
Subject: Wood Shop Classroom Classification of Hazard

I interpret the hazard classification of 3000sqft Wood Shop Classroom 
(High/Middle School) as Ordinary II - Wood Machining/Wood Product Assembly.  I 
was told that I was incorrect in my classification since it was a classroom and 
not a Woodshop Facility.  I can not find justification in the standards to down 
grade the hazard classification to Light or Ordinary I  just because the room 
is a classroom.  Am I missing something?  NFPA 13, 2010ed and IBC 2012

Sincerely,
Joe Kuerzi Jr., SET

           Certified Protection Services LLC
                  175 Sky Aire Rd. NW
                   Corydon, IN 47112

 Fire Protection & Water Back-flow Prevention Systems
   Installation, Maintenance, Repair, & Inspections

Contact - Joseph C. Kuerzi Jr., SET
812-738-2970 office
502-551-8530 mobile *preferred
[email protected]<mailto:[email protected]>
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=GV9x52NVphDNsWHM5QokaLumr6hpYXTeynUOAypTGXk&s=S4pTAkCBlvSSlKqf_9PKE9CDSPCxOW775TQzzEPe0Ac&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to