UG FW forumites,

Not sure if any of you are aware of this but NFPA 24 (2016) edition requires 
HDPE piping materials to be selected from AWWA C906 per Table 10.1.1.  NFPA 24 
Section 2.3.3 specifically references the 2007 edition of AWWA C906.  In AWAA 
C906 (2007), PE 4710 is not available. The allowable resins in this standard 
are/were PE 2406, PE 3406, and PE3408.

To comply with this, when actually purchasing the HDPE for fire water service, 
we have been stipulating, and being supplied with, PE4710 (previously 
dual-certified to PE 3408 including FM approvals matching those of PE3408) for 
as long as I can remember.  FM 1613 Approval Standard dated 12/31/17 has 
finally recognized the improved hydrostatic design stress characteristics of 
this resin and reclassified PE 4710 resin pressure classifications matching 
those the manufacturers had been stating from some time.  PE 3408 is being or 
has already been phased out per our known manufacturers now only making/using 
PE 4710 resins in HDPE piping and fitting production.

Since the 2016 edition of NFPA 24 still only recognizes AWWA C906 (2007), we 
are having to take the FM-approval as 'overruling' the Standard in this 
instance or else we are having difficulty writing spec language that allows us 
to provide PE 4710 for fire protection service because the NFPA 24 does not yet 
'allow' for this resin.

Have any of you run into this?

Do you know if NFPA 24 will be updated so that the 2015 edition of AWWA C906, 
which does include reference to PE 4710 resins (and others), will be acceptable?

Regards,

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Senior Fire Protection Engineer, Fire Protection Engineering Group
O 952-656-3662 \  M 320-250-5404 \  F 952-229-2923
[email protected]<mailto:[email protected]>  \  
burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 300  \  Bloomington, MN 55437

[cid:[email protected]]<https://www.linkedin.com/company/burns-&-mcdonnell>
  [cid:[email protected]] 
<https://www.facebook.com/BurnsMcDonnell>   
[cid:[email protected]] <https://twitter.com/BurnsMcDonnell>   
[cid:[email protected]] <https://www.youtube.com/user/burnsmcd>   
[cid:[email protected]] <http://www.burnsmcdblog.com/>   
[cid:[email protected]] 
<https://www.linkedin.com/profile/public-profile-settings?trk=prof-edit-edit-public_profile>
Proud to be one of FORTUNE's 100 Best Companies to Work For
Please consider the environment before printing this email.
*Registered in: LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout
This email and any attachments are solely for the use of the addressed 
recipients and
may contain privileged client communication or privileged work product. If you 
are not the
intended recipient and receive this communication, please contact the sender by 
phone at
816-333-9400, and delete and purge this email from your email system and 
destroy any
other electronic or printed copies. Thank you for your cooperation.
[Logo_1_Primary_2Color_sm]
Create Amazing.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to