The 1” to 6”  with the maximum of 22” requirements have been with us since they 
introduced the obstructed construction concept in the 1991 edition of NFPA 13.

Prior to that, the requirement for beam and girder construction was for 
sprinklers under beams to be 1” to 4” with a maximum of 20”.

Best regards,

Larry Keeping

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Reed A. Roisum, SET
Sent: April-27-18 12:48 PM
To: [email protected]
Subject: Concrete Pan Construction

I have existing sprinklers under concrete pan (obstructed) construction that 
are located 22” below the deck.  My concern is that the “beams” are 10” deep.  
That means the deflectors are not within 1-6” of the bottom of the structural 
member.  Am I not applying the correct arrangement from NFPA 13, 2013 ed. 
8.6.4.1.2?  I believe (1) is the only arrangement that works for this scenario. 
 Was the 1-6” below the bottom of the structural member added in recent years?

Thank you.

Reed Roisum


Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>