What are you waiting for.....

1) Request a written Notice of Violation which requires the adopted code 
citation(s).

2) Review the NOV and determine if code citation is correct, if a) if correct 
then advise client and comply if b)  not correct than;

3) File Notice of Appeal to the respective entity that handles appeals. Argue 
the incorrect citation demonstrating the correct code section.

4) Alternatively some state agency's have a regulatory bureau that hears 
complaints about inspectors, but again be certain you are correct else the 
issue could be sent to the sprinkler contractor licensing board for a 
compentency hearing.

In closing if the client does not want to do this then comply with the notice 
right or wrong. The power is in the clients hands to uphold the code. Before 
everyone chimes in I understand the part about not pissing off inspectors but 
the choice is yours.  Last but not least before throwing that rock be sure your 
house isn't made of glass.

John



John Drucker
Fire & Electrical Subcode Official
Borough of Red Bank, NJ
Cell/Text 732-904-6823
On May 9, 2018 17:49, "Mark.Phelps" <mphe...@aerofire.com> wrote:
I do it for the pure unadulterated sport of it. “For the Love of the Game”. 
Somehow the thought of getting paid for doing it would make me feel like a 
pros… well, it just wouldn’t be the same!! ;-)


Mark at Aero
602 820-7894

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: Wednesday, May 09, 2018 2:16 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] RE: Non-Combustible Concealed Space (NFPA 13 2013)

Absolutely.   What could be a better gig than GETTING PAID to fight with fire 
officials??

Steve

PS:  No guarantee of result.  Side effects include lingering hard feelings.

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Rocci 3 Cetani
Sent: Wednesday, May 09, 2018 1:13 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Non-Combustible Concealed Space (NFPA 13 2013)

Steve can I hire you to fight with AHJ’s when I have issues?

Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III

Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590


roc...@norcalfire.com<mailto:roc...@norcalfire.com>
www.norcalfire.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.norcalfire.com_&d=DwMGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=n8M9K6LvsalnCHEvYE1b8Lw5A8ZNxnzU0niijnqyoPo&s=35p-Y2NwvQx-UgogtCyOv9CfmqRvaO00ZR16HTmK0PI&e=>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information
belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Steve Leyton
Sent: Wednesday, May 09, 2018 12:00 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Non-Combustible Concealed Space (NFPA 13 2013)

Noooooooooooo!!!!   Let’s stop using the word “accessible” in conjunction with 
T-Bar ceilings.   As described in the standard for purposes of determining 
whether a non-combustible space might require sprinklers or not, the concept of 
accessible is in the context of occupancy.   Is the space accessible FOR 
OCCUPANCY.    Putting your head into an interstitial space most certainly does 
NOT make it accessible for occupancy.  If there’s a suspended, load-bearing 
platform that you can store or stand on, then it’s accessible.   If there’s a 
heater in that space that’s suspended from the deck, then obviously you can 
access the equipment for service, but it’s not occupied or accessible in the 
sense that you would have to fire protect for some other use than “Unused 
Attic” as it’s described in Chapter 5.   That the appliance is gas-fired adds a 
twist to the conversation, but not so profoundly that a single upright 
sprinkler at the unit wouldn’t address that concern.

Occupancy = fire load.   If it doesn’t have measurable fire load, it doesn’t 
matter if you can “access” it from a  ladder.  We have to deal with this crap 
all the time with state agencies here in CA and it’s exhausting …

SML

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jay Stough
Sent: Wednesday, May 09, 2018 8:25 AM
To: Sprinkler Forum
Subject: Re: Non-Combustible Concealed Space (NFPA 13 2013)

It is accessible thru the suspended ceiling with ladders.

Jay Stough
NICET IV LAYOUT
NICET III ITM


On Wed, May 9, 2018 at 11:04 AM Casey Yardley 
<cj.yardle...@gmail.com<mailto:cj.yardle...@gmail.com>> wrote:
Jay,

  Are the non combustible concealed spaces readily accessible or no?



From: Jay Stough<mailto:jaycs7...@gmail.com>
Sent: Wednesday, May 9, 2018 8:00 AM
To: Sprinkler Forum<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Non-Combustible Concealed Space (NFPA 13 2013)

We are bidding a school gym/locker rooms project that has non-combustible 
concealed spaces above the ceilings.  Most of the HVAC equipment is on the 
roof, but there is one gas fired unit in that concealed space in one area.  I 
cannot find where I have to install sprinklers in that area due to the unit, 
but it does not feel right eliminating them.  If I put sprinklers above the 
ceiling in this area, it would still be about half the building.  I know I am 
missing something in 8.15, so can anyone help?  Thanks!

Jay Stough
NICET IV LAYOUT
NICET III ITM

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=n8M9K6LvsalnCHEvYE1b8Lw5A8ZNxnzU0niijnqyoPo&s=Q3LiCo8x6viDF7fjO0Ldo1q-RkifbNSDl2AedOtIwAc&e=>