UL listed for the ceiling grid. That should more than suffice.

On Wed, May 30, 2018 at 10:59 AM, Richard Mote <[email protected]>
wrote:

> I have a AHJ that is questioning the use of Flex Drops especially the
> Victaulic ones. He says that they are so flexible that when a sprinkler
> goes off the jet effect is going to lift the sprinkler up through the
> ceiling. I told him that the drops are mechanically attached to the ceiling
> grid and in order to lift up they would have to lift the entire weight of
> the ceiling grid, ceiling tiles, the lights and HVAC diffusers. His answer
> prove, it either by letter from the manufacturer or from someone a lot
> higher up the food chain than either he or I am. Or something specific
> in NFPA 13 that says he is wrong.
>
>
> *Richard Mote*
>