Is there any No No's to mix different ESFR K factors on a project.

My situation is that I have 8 zones fed from the far end of a building,

if I use K22's it requires 40 psi end head pressure and K16.8 uses

63 psi. The farthest two zones require some 8" feed mains, the last six

zones can work with 6" feed mains using all K22 ESFR's.


Now I can get the last three zones to work with K16.8 ESFR's with

6" feed mains.


Using both is more economical.


Mike