You are not mixing sprinklers within the system to balance hydraulics.  You
are using math to find the most hydraulically efficient system.  I do not
have a problem with it.  It is a perfectly logical thing to do.  I really
like the difference in weld-o-let sizes.  You won't put the wrong head in a
system.  

 


Nick Maneen, SET 

c 704.791.7789

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Mike Hairfield
Sent: Tuesday, June 05, 2018 9:56 AM
To: Sprinkler Forum
Subject: Mixing ESFR Sprinklers

 

Is there any No No's to mix different ESFR K factors on a project.

 

My situation is that I have 8 zones fed from the far end of a building,

if I use K22's it requires 40 psi end head pressure and K16.8 uses

63 psi. The farthest two zones require some 8" feed mains, the last six

zones can work with 6" feed mains using all K22 ESFR's.

 

Now I can get the last three zones to work with K16.8 ESFR's with

6" feed mains.

 

Using both is more economical.

 

Mike