Unless someone manually closes the PIV, how is an open valve going to stop 
backflow?

John
 
John August Denhardt, P.E.
Strickland Fire Protection Incorporated
4011 Penn Belt Place
Forestville, Maryland 20747-4737
301.474.1136 - Office
301.343.1457 - Mobile
-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Prahl, Craig/GVL
Sent: Monday, July 9, 2018 11:27 AM
To: [email protected]
Subject: RE: 2013 NFPA 13, Figure A.8.16.1.1 Check valve in supply 

When that reason was presented to the designer they stated that's what the PIV 
on the UG was for.  To isolate the UG from the AG system.

Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252 | 
[email protected] | www.jacobs.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Denhardt
Sent: Monday, July 09, 2018 10:39 AM
To: [email protected]
Subject: [EXTERNAL] RE: 2013 NFPA 13, Figure A.8.16.1.1 Check valve in supply 

Exactly.

Thanks,
John
 
John August Denhardt, P.E.
Strickland Fire Protection Incorporated
4011 Penn Belt Place
Forestville, Maryland 20747-4737
301.474.1136 - Office
301.343.1457 - Mobile

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Richard Carr
Sent: Monday, July 9, 2018 10:38 AM
To: [email protected]
Subject: RE: 2013 NFPA 13, Figure A.8.16.1.1 Check valve in supply 

I have always thought the check valve was to so the FDC did not pump up the 
underground.

Richard M. Carr, SET
Project Manager/Design
Diboco Fire Sprinklers, Inc.
325 Jackson Loop Road
Flat Rock, NCĀ  28731

[email protected]
828-696-3400
828-696-2288 Fax
828-708-9118 Mobile






-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Prahl, Craig/GVL
Sent: Monday, July 09, 2018 10:34 AM
To: [email protected]
Subject: 2013 NFPA 13, Figure A.8.16.1.1 Check valve in supply 

Having a discussion with a designer concerning a manifolded riser assembly 
which has a dry pipe system and wet pipe system as shown in 2013 NFPA 13, 
Figure A.8.16.1.1.  The question is the purpose of the check valve in the 
portion below the split at the manifold.  Their FDC is piped in accordance with 
the detail.  The designer says the check valve in the vertical is not needed 
because they are on a non-potable water supply and they have a PIV outside.

Thoughts, opinions?

Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252 | 
[email protected] | www.jacobs.com

________________________________________________________________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIFAw&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=MIyv3E2h5_6bDxuz4mKDKbGlpUL2hNWwltHyMeMVZsY&s=rP1gn3mNbmZ2b-Rjkl4sdxzEZTemTYvi4gejV-TbxNY&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIFAw&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=MIyv3E2h5_6bDxuz4mKDKbGlpUL2hNWwltHyMeMVZsY&s=rP1gn3mNbmZ2b-Rjkl4sdxzEZTemTYvi4gejV-TbxNY&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIFAw&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=MIyv3E2h5_6bDxuz4mKDKbGlpUL2hNWwltHyMeMVZsY&s=rP1gn3mNbmZ2b-Rjkl4sdxzEZTemTYvi4gejV-TbxNY&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to