Perhaps.   If it’s supplying a standpipe system, a single PRV is not acceptable.

[Steve Signature (3)]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Fire Design
Sent: Friday, July 13, 2018 3:32 PM
To: [email protected]
Subject: Re: PRV after pump discharge control valve

No, it's all good after the pump discharge control valve.
A.4.7.7.2


On Fri, Jul 13, 2018 at 3:03 PM, Dewayne Martinez 
<[email protected]<mailto:[email protected]>> wrote:
Is there anything that restricts the use of a PRV after the discharge control 
valve on a fire pump?
I have a ESFR storage building where I am designing to a “future” water supply 
which is much higher than the existing water supply.
The fire pump must satisfy both existing and future conditions and I thought 
about leaving a space for a PRV to be installed downstream of the pump 
discharge valve to account for the future higher pressures.
Thanks,

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]<mailto:[email protected]>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/

[A close up of a sign    Description generated with high confidence]