As with some of your previous posts, I've read and re-read this one and taken a 
few days to process it before responding.  And having given this some thought, 
I have to ask:  what is the point of undertaking this?   Obviously, no fitter 
or service tech is going to change out an impeller - what do you think the cost 
of a factory-certified or an actual factory tech doing such a service might be? 
  What cost benefit could there possibly be that justifies the hassle and risk 
of having someone rebuild a listed pump on site, especially when there are 
other "conventional" resolutions available?

Unless ... you just have an uncontrollable compulsion to post equations on 
line?  Perhaps we can (should?) change the name of this list-server to the 
"AFSA Sprinkler Formulae" ...

Steve Leyton
Keepinit Simple, CA

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Saturday, July 14, 2018 1:12 PM
To: [email protected]
Subject: Re: PRV after pump discharge control valve

This is very interesting Dewayne!
You need a high pressure pump now--low pressure pump later, but since  
you have to keep the original pump you are thinking PRV on the  
discharge later.

There might be another way:

Replace the big impeller now with a small impeller later. I know how  
to make it work in theory but I'm not sure if it works in application,  
but the pump rep would.
I know it works in theory because I figured out quite a few years ago  
how to calculate the impeller diameter based on the rated psi and rpm  
ONLY.
I do know it is not unheard of to 'trim' an installed impeller to tamp  
down on the psi.

v=2*pi*r*f, where,

v is velocity (ft/s) calculated from feet of head (h). v=SQRT(2gh), g  
is 32.2 ft/s/s.
r is the impeller radius (ft).
f is radian/s (rpm/60).

So knowing v and f, it's easy to rearange to solve for r!!!

You should still install a spool piece I guess, but to pump it up only  
to let the air out a couple feet later never has made sense to me.

Maybe Nicky in NZ knows of something in the European Code that might  
shed a different light?

Brad


Quoting Dewayne Martinez <[email protected]>:

> Is there anything that restricts the use of a PRV after the discharge
> control valve on a fire pump?
>
> I have a ESFR storage building where I am designing to a “future” water
> supply which is much higher than the existing water supply.
>
> The fire pump must satisfy both existing and future conditions and I
> thought about leaving a space for a PRV to be installed downstream of the
> pump discharge valve to account for the future higher pressures.
>
> Thanks,
>
>
>
> Dewayne Martinez
>
> Fire Protection Design Manager
>
>
>
> *TOTAL* *Mechanical*
>
> *Building* *Integrity*
>
>
> W234 N2830 Paul Rd.
> Pewaukee, WI  53072
>
> [email protected]
>
> Ph:  262-522-7110
>
> Cell: 414-406-5208
>
> http://www.total-mechanical.com/
>
>
>
> [image: A close up of a sign Description generated with high confidence]



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to