If you've already got a diesel pump, the cost increase is reasonable. Upgrading 
from an electric fire pump to a diesel PLD is a pretty large financial 
commitment.

Also, there are limits to how much the PLD can limit the pressure (poor word 
choice). There is a PLD calculator that you (or pump rep can use) to determine 
if the PLD will do what you want. The O.P. never said what the expected 
pressure differential was going to be, but if it is very large the PLD may not 
be an option. For example, if your static pressure plus churn is up over 250 
psi or so, you probably won't be able to limit the output it to under 175 psi 
(the diesel engine can only reliably idle so low).

But the diesel PLD is my favorite option, all other things considered.

-Kyle M

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Denhardt
Sent: Monday, July 16, 2018 12:27 PM
To: [email protected]
Subject: [EXTERNAL] RE: PRV after pump discharge control valve

I've personally have installed several PLD with great success.  Diesel driven 
is the way to go.  Cost increase was reasonable.

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Steve Leyton
Sent: Monday, July 16, 2018 3:20 PM
To: [email protected]
Subject: RE: PRV after pump discharge control valve

I thought of it too, but it's expensive and they've got a janky service record 
so far (high maintenance, very expensive parts and service, parts availability 
issues).   I think the reducing valve is the way to go, with special emphasis 
on the system being ITM'd per the book.

SML

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mitchell, Scott
Sent: Monday, July 16, 2018 12:18 PM
To: [email protected]
Subject: RE: PRV after pump discharge control valve

I too was thinking of a Variable Frequency Pressure Limiting Controller 
(VFPLC), but hesitated for fear of ridicule.  Mr. Denhardt has no fear.

J. Scott Mitchell, P.E.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Denhardt
Sent: Monday, July 16, 2018 1:55 PM
To: [email protected]
Subject: RE: PRV after pump discharge control valve

What about looking at a pressure limiting driver fire pump system?  These are 
increasing more commonly available and Listed from the factory for this 
application.

In my humble opinion, the cost involved in modifying an impeller and the 
liability associated with it, makes this approach not practical.

John
 
John August Denhardt, P.E.
Strickland Fire Protection Incorporated
4011 Penn Belt Place
Forestville, Maryland 20747-4737
301.474.1136 - Office
301.343.1457 - Mobile

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Kyle.Montgomery
Sent: Monday, July 16, 2018 2:47 PM
To: [email protected]
Subject: RE: PRV after pump discharge control valve

I found the formula interesting.

Also, I didn't think that Brad was suggesting the fitter would modify the 
impeller (were you?). I assumed he was just showing that it was another 
possibility to explore (to be performed by pump rep). You wouldn't modify the 
existing impeller, but replace it with a new one.

I do know it is possible (and not entirely uncommon) to have the pump 
manufacturer "trim" the impeller to make small modifications to the pump curve, 
to dial in the pressure. Not sure if it would work for the kind of pressure 
differences the O.P. is looking at.

If it is feasible, I think that (generally speaking) it might be considered a 
preferable approach to the PRV. Less parts and pieces, etc. However, the nice 
thing about a PRV is you can really dial in the pressure and you get that wide, 
flat pressure curve. But there are drawbacks as well.

Kyle Montgomery
 
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Denhardt
Sent: Monday, July 16, 2018 10:36 AM
To: [email protected]
Subject: [EXTERNAL] RE: PRV after pump discharge control valve

I agree with Steve.  No manufacturer or Listing agency would accept this 
approach.  This is a purely academic exercise which it my opinion has no basis 
for real world application.  My suggestion is to move on.

John
 
John August Denhardt, P.E.
Strickland Fire Protection Incorporated
4011 Penn Belt Place
Forestville, Maryland 20747-4737
301.474.1136 - Office
301.343.1457 - Mobile


-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Steve Leyton
Sent: Monday, July 16, 2018 12:42 PM
To: [email protected]
Subject: RE: PRV after pump discharge control valve

As with some of your previous posts, I've read and re-read this one and taken a 
few days to process it before responding.  And having given this some thought, 
I have to ask:  what is the point of undertaking this?   Obviously, no fitter 
or service tech is going to change out an impeller - what do you think the cost 
of a factory-certified or an actual factory tech doing such a service might be? 
  What cost benefit could there possibly be that justifies the hassle and risk 
of having someone rebuild a listed pump on site, especially when there are 
other "conventional" resolutions available?

Unless ... you just have an uncontrollable compulsion to post equations on 
line?  Perhaps we can (should?) change the name of this list-server to the 
"AFSA Sprinkler Formulae" ...

Steve Leyton
Keepinit Simple, CA

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Saturday, July 14, 2018 1:12 PM
To: [email protected]
Subject: Re: PRV after pump discharge control valve

This is very interesting Dewayne!
You need a high pressure pump now--low pressure pump later, but since you have 
to keep the original pump you are thinking PRV on the discharge later.

There might be another way:

Replace the big impeller now with a small impeller later. I know how to make it 
work in theory but I'm not sure if it works in application, but the pump rep 
would.
I know it works in theory because I figured out quite a few years ago how to 
calculate the impeller diameter based on the rated psi and rpm ONLY.
I do know it is not unheard of to 'trim' an installed impeller to tamp down on 
the psi.

v=2*pi*r*f, where,

v is velocity (ft/s) calculated from feet of head (h). v=SQRT(2gh), g is 32.2 
ft/s/s.
r is the impeller radius (ft).
f is radian/s (rpm/60).

So knowing v and f, it's easy to rearange to solve for r!!!

You should still install a spool piece I guess, but to pump it up only to let 
the air out a couple feet later never has made sense to me.

Maybe Nicky in NZ knows of something in the European Code that might shed a 
different light?

Brad


Quoting Dewayne Martinez <[email protected]>:

> Is there anything that restricts the use of a PRV after the discharge 
> control valve on a fire pump?
>
> I have a ESFR storage building where I am designing to a “future” 
> water supply which is much higher than the existing water supply.
>
> The fire pump must satisfy both existing and future conditions and I 
> thought about leaving a space for a PRV to be installed downstream of 
> the pump discharge valve to account for the future higher pressures.
>
> Thanks,
>
>
>
> Dewayne Martinez
>
> Fire Protection Design Manager
>
>
>
> *TOTAL* *Mechanical*
>
> *Building* *Integrity*
>
>
> W234 N2830 Paul Rd.
> Pewaukee, WI  53072
>
> [email protected]
>
> Ph:  262-522-7110
>
> Cell: 414-406-5208
>
> https://urldefense.proofpoint.com/v2/url?u=http-3A__www.total-2Dmechan
> ical.com_&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3b
> n8etxB7nLN8OBJwQd9A&m=FU1ekxtEezMunTSmi6Q7K68HzkOxQ8TohV5jBLKF6mw&s=bx
> fEUpUsyf9DVMeiFuKDDoGheRtiHWc6jtv2vKtqIWE&e=
>
>
>
> [image: A close up of a sign Description generated with high 
> confidence]



_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=FU1ekxtEezMunTSmi6Q7K68HzkOxQ8TohV5jBLKF6mw&s=CnrCn1hZdkdLJl9g9My8X3gWvSN2uJ1DXkqStfBxCNk&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=FU1ekxtEezMunTSmi6Q7K68HzkOxQ8TohV5jBLKF6mw&s=CnrCn1hZdkdLJl9g9My8X3gWvSN2uJ1DXkqStfBxCNk&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=FU1ekxtEezMunTSmi6Q7K68HzkOxQ8TohV5jBLKF6mw&s=CnrCn1hZdkdLJl9g9My8X3gWvSN2uJ1DXkqStfBxCNk&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=7LzSN5fEThQKKcnideyNWGGwMQYPXF5rSMkfm_vhAC4&s=mXtRSn7I1Dbro257OhTNZQvFl9TvbuafswDK7Gr7DVA&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=7LzSN5fEThQKKcnideyNWGGwMQYPXF5rSMkfm_vhAC4&s=mXtRSn7I1Dbro257OhTNZQvFl9TvbuafswDK7Gr7DVA&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=7LzSN5fEThQKKcnideyNWGGwMQYPXF5rSMkfm_vhAC4&s=mXtRSn7I1Dbro257OhTNZQvFl9TvbuafswDK7Gr7DVA&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=7LzSN5fEThQKKcnideyNWGGwMQYPXF5rSMkfm_vhAC4&s=mXtRSn7I1Dbro257OhTNZQvFl9TvbuafswDK7Gr7DVA&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=7LzSN5fEThQKKcnideyNWGGwMQYPXF5rSMkfm_vhAC4&s=mXtRSn7I1Dbro257OhTNZQvFl9TvbuafswDK7Gr7DVA&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to