Reed yes. The IFC does have a definition for a limited spray space. That's nine 
square feet or less. If it looks like a duck.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Reed A. Roisum, SET
Sent: Wednesday, July 25, 2018 9:00 AM
To: [email protected]
Subject: Paint Booths

Is a paint booth, regardless of size, treated the same as a spray booth from 
NFPA 13/33?  I have a small paint booth (1 head plus the exhaust duct), and I 
just want to verify that I am to meet the requirements of NFPA 13, 2010 edition 
21 .4 Spray Application Using Flammable or Combustible Materials, which is 
taken from NFPA 33?
EH2, separate valve, cellophane or paper bags over the sprinklers, sprinklers 
in stacks or ducts spaced every 12', etc.

Thank you.