You might be interested to know that the NFPA 13 Installation TC considered a 
proposal 13-122 for larger system sizes in the ROP meeting for the development 
of NFPA 13-2010. The TC rejected that proposal and issued a committee statement:

“System size limits have a long and successful history that the committee is 
reluctant to change. The potential for much larger systems to be out of service 
during testing, inspections and maintenance events speaks against increasing 
system sizes.”

Larry Keeping

From: Sprinklerforum <[email protected]> On Behalf 
Of Matt Grise
Sent: August-14-18 5:20 PM
To: [email protected]
Subject: maximum sprinkler system sizes

I was recently discussing the max system size issue with a building official. 
In this specific application we are requesting that the AHJ allow us to use a 
60,000 square foot maximum size for ESFR systems in a big box warehouse.

I have commentary directly from FM (in addition to FM2-0) that says “The size 
of the sprinkler system is not expected to affect the effectiveness of the 
sprinkler system as long as the system is designed properly for the occupancy.”

The AHJ’s response was: “The system will work as well when the system is in 
operation, but when you turn it off for maintenance, there is a greater risk of 
fire since there is more area out of service.”

I had assumed that the greater system sizes result in equal system 
effectiveness on the whole – in the sense that there is no evidence that the 
greater system area causes more fire losses even when maintenance downtime is 
factored into the equation. I had even thought that perhaps system performance 
on the whole would be improved since there are fewer control valves in the 
building that could be left closed (when they should be open).

But, I have heard that “assuming” things can have negative consequences…

On that note, I wanted to reach out and see what insight anyone might offer on 
system performance related to system size. Do large sprinkler systems perform 
equally only when they are operating properly – or do they operate properly 
(and perform equally) just as well, historically, as smaller systems? Has 
larger system size ever been faulted as the cause of a loss?

Any insight/research/documentation would be great!

Thanks,

Matt