I recommend that someone keep submitting a PI to increase the system size 
limitations. One cycle, the committee will go “hey” that is a great idea. I’ve 
seen it happen over the last 4 NFPA 13 cycles. Did I mention single point 
density…. DOH

From: Sprinklerforum <[email protected]> On Behalf 
Of Ron Greenman
Sent: Wednesday, August 15, 2018 1:37 PM
To: [email protected]
Subject: Re: maximum sprinkler system sizes

And the myth of 52K is OK, but 60K is too big, but two levels of 52K aren't too 
big so the myth persists. I'd agree that what we've done in the past has worked 
and that's a decent criterion for making a determination but it's also akin to 
saying I don't need sprinklers because I've never had a fire before. If the 
limitations are tied to the limitation of the pipe schedule then it stands to 
reason that with the near-universal use of hydraulic instead of pipe scheduling 
any numbers that are tied to that schedule may or may not be efficacious and 
new criteria may be appropriate.


Ron Greenman

[email protected]<mailto:[email protected]>

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)


On Wed, Aug 15, 2018 at 5:47 AM Larry Keeping 
<[email protected]<mailto:[email protected]>> wrote:
You might be interested to know that the NFPA 13 Installation TC considered a 
proposal 13-122 for larger system sizes in the ROP meeting for the development 
of NFPA 13-2010. The TC rejected that proposal and issued a committee statement:

“System size limits have a long and successful history that the committee is 
reluctant to change. The potential for much larger systems to be out of service 
during testing, inspections and maintenance events speaks against increasing 
system sizes.”

Larry Keeping

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Matt Grise
Sent: August-14-18 5:20 PM
To: 
[email protected]<mailto:[email protected]>
Subject: maximum sprinkler system sizes

I was recently discussing the max system size issue with a building official. 
In this specific application we are requesting that the AHJ allow us to use a 
60,000 square foot maximum size for ESFR systems in a big box warehouse.

I have commentary directly from FM (in addition to FM2-0) that says “The size 
of the sprinkler system is not expected to affect the effectiveness of the 
sprinkler system as long as the system is designed properly for the occupancy.”

The AHJ’s response was: “The system will work as well when the system is in 
operation, but when you turn it off for maintenance, there is a greater risk of 
fire since there is more area out of service.”

I had assumed that the greater system sizes result in equal system 
effectiveness on the whole – in the sense that there is no evidence that the 
greater system area causes more fire losses even when maintenance downtime is 
factored into the equation. I had even thought that perhaps system performance 
on the whole would be improved since there are fewer control valves in the 
building that could be left closed (when they should be open).

But, I have heard that “assuming” things can have negative consequences…

On that note, I wanted to reach out and see what insight anyone might offer on 
system performance related to system size. Do large sprinkler systems perform 
equally only when they are operating properly – or do they operate properly 
(and perform equally) just as well, historically, as smaller systems? Has 
larger system size ever been faulted as the cause of a loss?

Any insight/research/documentation would be great!

Thanks,

Matt

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to