On a seismic job, I have always designed such that there is either a flexible 
drop or a hole 1" larger than required for the sprinkler head in gypsum board 
ceilings.  I was thinking that practice was based on NFPA 13, but as I look for 
it now, I do not see it.  Instead, it appears this requirement is found in ASCE 
7.


While NFPA 13 says nothing of ASCE 7 regarding seismic protection, the IBC 
states that all non-structural components be protected in accordance with ASCE 
7.  As I understand it, the protection requirements of NFPA 13 were developed 
to comply with the ASCE 7 requirements.  Soooo, my question is, am I required 
to provide this 1" clearance at sprinkler drops in rigid ceilings or does NFPA 
13's silence mean I am not held to this?