Thank you, Ken.  That is extremely helpful.

Micah Davis, SET
NICET #124745
Water Based Systems Layout, Level IV    Dynamic Fire Designs

Mail: [email protected]
Mobile: 931-242-1299
www.dynamicfiredesigns.com<http://dynamicfiredesigns.com>


Dynamic Fire Designs • 247 Winthrop Dr. • Spring Hill • FL • 34609

This message is confidential. It may also be privileged or otherwise protected 
by work product immunity or other legal rules. If you have received it by 
mistake, please let us know by e-mail reply and delete it from your system; you 
may not copy this message or disclose its contents to anyone. The integrity and 
security of this message cannot be guaranteed on the Internet.



________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Parsley Consulting <[email protected]>
Sent: Friday, August 17, 2018 1:11 PM
To: [email protected]
Subject: Re: Clearance @ Sprinkler in Seismic Area

Micah,

The requirement for clearance between the hole for a pendent sprinkler and the 
adjacent ceiling around that penetration is clearly identified in ASCE/SEI 7.

Specifically, those requirements are:

  *   In the event that the suspended ceilings are not rigidly braced per ASME 
E580, the sprinklers are to be installed in the suspended panels with either a 
2” clearance around the penetration through the panel, or the use of a flexible 
drop fitting, per ASCE7-10, section 13.5.6.2.1 through 15.6.3
     *   Please note that this reference to a "flexible drop fitting" does not 
refer to a drop to a sprinkler with a flexible coupling at some point in the 
drop. Rather it refers to a device like that from Flex-Head, AquaFlex, 
Victaulic or other manufacturers which hold the sprinkler tight in a bracket 
where the sprinkler moves with the ceiling.

  *   Suspended ceilings with areas less than or equal to 144 ft² that are 
surrounded by walls or soffits that are laterally braced to the structure above 
are exempt from this requirement

  *   Suspended ceilings constructed of screw or nail attached gypsum board on 
one level that are surrounded by and connected to walls or soffits that are 
laterally braced to the structure above are exempt from these requirements

We could argue the semantics that the hole only needs to be 1" larger vs. a 2" 
diameter hole, and I can testify that this argument has been made endlessly to 
me.


Now, my take on your question is this:  If that ceiling is rigidly braced per 
the parameters of ASME E580, then there is no need for you to provide either 
the 2" oversize ring or a flexible drop fitting.  I would suggest that it's the 
responsibility of the ceiling contractor to provide that information not yours. 
 Similarly, if you're dropping the sprinklers into a gyp board ceiling there's 
no additional requirement.


As I'm a member of the hanging and bracing committee, see the disclaimer below.

Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit the website<http://www.parsleyconsulting.com/>

IMPORTANT NOTICE: This correspondence is not a Formal Interpretation issued 
pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of 
the author and does not necessarily represent the official position of the NFPA 
or its Technical Committees. In addition, this correspondence is neither 
intended, nor should it be relied upon, to provide professional consultation or 
services

It should be noted that the above is my opinion as a member of the NFPA 
Automatic Sprinkler System Hanging and Bracing Committee in accordance with the 
NFPA Regulations Governing Committee Projects and should therefore not be 
considered, nor relied upon, as the official position of the NFPA or its 
Committees

On 08/17/2018 10:00 AM, Micah Davis, SET wrote:

On a seismic job, I have always designed such that there is either a flexible 
drop or a hole 1" larger than required for the sprinkler head in gypsum board 
ceilings.  I was thinking that practice was based on NFPA 13, but as I look for 
it now, I do not see it.  Instead, it appears this requirement is found in ASCE 
7.


While NFPA 13 says nothing of ASCE 7 regarding seismic protection, the IBC 
states that all non-structural components be protected in accordance with ASCE 
7.  As I understand it, the protection requirements of NFPA 13 were developed 
to comply with the ASCE 7 requirements.  Soooo, my question is, am I required 
to provide this 1" clearance at sprinkler drops in rigid ceilings or does NFPA 
13's silence mean I am not held to this?


Micah Davis, SET
NICET #124745
Water Based Systems Layout, Level IV    Dynamic Fire Designs

Mail: 
[email protected]<mailto:[email protected]>
Mobile: 931-242-1299
www.dynamicfiredesigns.com<http://dynamicfiredesigns.com>


Dynamic Fire Designs • 247 Winthrop Dr. • Spring Hill • FL • 34609

This message is confidential. It may also be privileged or otherwise protected 
by work product immunity or other legal rules. If you have received it by 
mistake, please let us know by e-mail reply and delete it from your system; you 
may not copy this message or disclose its contents to anyone. The integrity and 
security of this message cannot be guaranteed on the Internet.




_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to