Is this in California?  The IBC is somewhat vague, but the California DSA 
text specifically calls out "designed for human occupancy".  Generally a 
splice vault is a small prefab enclosure designed for terminating data 
cabling, and would not fit the definition of designed for human occupancy. 
 But obviously your projects conditions/size of vault may vary.  My 
opinion only, 



Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]







From:   "Jerry Van Kolken" <[email protected]>
To:     <[email protected]>
Date:   08/28/2018 07:28 PM
Subject:        When is it a Floor?
Sent by:        "Sprinklerforum" 
<[email protected]>



BE ADVISED - This email originated outside EMCOR. 

I have a 2 story building with a 600sqft “Splice Vault” underneath it. The 
reviewer is calling this out as basement, hence 3 stories, which would 
require floor controls. In 13-8.2.4 (2016) it discuss floor controls not 
being required in apartment situations, and floor areas above, but nothing 
for below. Is there any references I could look at to not have to install 
extra floor controls?
 
Jerry Van Kolken
Millennium Fire Protection Corp.
2950 San Luis Rey Rd.
Oceanside, CA 92058
(760) 722-2722 FX 722-2730
 _______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=zZkTQAM1PsnaOfyHGjdaXtUWHk8Hip0ZBuZuvvalm9c&s=Ejak7pegUyp4pLbkAQIVZnG9g_e3o_rKlozSu6z8bTo&e=




This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to