That is quite clear – thanks.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Taylor Schumacher
Sent: Monday, September 24, 2018 10:52 AM
To: [email protected]
Subject: RE: Omission of sprinklers in hotel bathrooms

NFPA 13 3.3.2 “two bathrooms can be adjacent to each other and are considered 
separate rooms, provided they are enclosed with the required level of 
construction.”


Taylor Schumacher

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Fox, Duane T. (FireMarshal)
Sent: Monday, September 24, 2018 9:48 AM
To: '[email protected]'
Subject: Omission of sprinklers in hotel bathrooms

I have a hotel project where the designer has placed a door inside the bathroom 
between the sink and toilet/shower.  The bathroom is over 55 sqft, however, 
with the placement of the door inside the bathroom each area on either side of 
the door is less than 55 sqft.  NFPA 13 – 8.15.8.1 states bathrooms under 55 
sqft are exempt (with other criteria met) and the appendix for that section 
states a door is not required in order to omit sprinkler as long as the 
bathroom complies with the definition for compartment. I assume the door in the 
appendix is between the bathroom and the living space.  My question: is adding 
a door inside the bathroom, making two areas within the bathroom, a viable 
design to allow the sprinklers to be omitted?

In my opinion the bathroom square footage is the entire area within the 
bathroom space no matter how many doors are used. Therefore, the space would 
need coverage.

Duane T. Fox, Jr., CFPS, CFI, CFPE
Asst Chief, Technical Services
DE State Fire Marshal’s Office
302-856-5298


_______________________________________________