There is actually some sense to this. Not because of the color, but just to 
make sure the ordinary temp heads don’t end up in the wrong location.

It’s no fun when you get a call from the fitter as he get near the top of a 
high-rise apartment that goes something like this: “I need to order more 
ordinary temp heads. For some reason, we only have intermediate temp for the 
last three floors.” And you know that you ordered the right amount of each…

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Shawn Foor
Sent: Friday, November 9, 2018 7:51 AM
To: [email protected]
Subject: Re: [EXTERNAL] RE: Sprinklers next to Diffusers

I have had an architect and ahjs ask for intermediate temp head throughout so 
there wouldn’t be two different color bulbs

On Fri, Nov 9, 2018 at 08:43 Kyle.Montgomery 
<[email protected]<mailto:[email protected]>> wrote:
Depends on how you read that table (6.2.5.1). The way I read it, says that you 
can only use ordinary temp heads if your maximum ceiling temperature is 100 
degrees or less.

And you can only use intermediate temperature heads if your maximum ceiling 
temperature is 150 degrees or less.

But it doesn’t say you can only use intermediate temp heads if your maximum 
temperature is between 100 and 150 degrees. If the maximum ceiling temperature 
is 85 degrees, that is still less than 150 degrees, so intermediate is OK.

I think a lot of people interpreted it incorrectly to mean you could ONLY use 
intermediate temperature if the max ceiling temp was above 100 degrees, which 
is why they added the language in 8.3.2.1.

Think about the fact that we can use high-temp heads in ordinary and extra 
hazard occupancies. Except during a fire, these areas probably aren’t seeing 
temperatures over 150 degrees, right?

But that still doesn’t totally solve the original poster’s problem, since he 
has to work off of table 8.3.2.5( c ) for residential heads, although it allows 
him to get a little closer.

-Kyle M

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of BJ Newlin
Sent: Friday, November 9, 2018 6:44 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] RE: Sprinklers next to Diffusers

Are you allowed to use intermediate sprinklers everywhere? In 13 Section 
8.3.2.1 seems to interchange the use of intermediate and ordinary, but table 
6.2.5.1 indicates that if the maximum ceiling temperature does not exceed 100° 
Ordinary sprinklers are to be used.

I know this is a gray area we take advantage of to ensure our fitters don’t 
have to look at what they’re installing, but is it technically in compliance 
with code?


B.J. Newlin
Service Sales
Aegis Fire Protection LLC.

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten. “--Benjamin Franklin

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of ron fletcher
Sent: Thursday, November 8, 2018 2:56 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Sprinklers next to Diffusers

Why not use intermediate temp heads everywhere? Then diffuser proximity won't 
matter.

Ron F

On Thu, Nov 8, 2018, 1:57 PM Kyle.Montgomery 
<[email protected]<mailto:[email protected]>> wrote:
What Steve said.

Generally, my experience has been that if they have a heat pump, max outlet 
temperature will be less than 100 degrees. But if they have a furnace, there is 
a good chance it will be higher. Mechanical designer/contractor should be able 
to answer the question.

-Kyle M

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Steve Leyton
Sent: Thursday, November 8, 2018 12:20 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] Re: Sprinklers next to Diffusers

Higher than the ambient temp rating of the subject sprinkler.



Steve Leyton

(Sent from my phone; please excuse typos and voice text corruptions.)



-------- Original message --------
From: Jerry Van Kolken <[email protected]<mailto:[email protected]>>
Date: 11/8/18 8:47 PM (GMT+03:00)
To: 
[email protected]<mailto:[email protected]>
Subject: Sprinklers next to Diffusers

NFPA 13-2016 Table 8.3.2.5 (c)

Reads

Side of ceiling- or wall-mounted hot air diffuser  Minimum Distance from Edge 
of Source to Ordinary-Temperature Sprinkler  - 24”

What is the temp of “Hot Air”?

Jerry Van Kolken
Millennium Fire Protection Corp.
2950 San Luis Rey Rd.
Oceanside, CA 92058
(760) 722-2722 FX 722-2730

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=pWaA7z6bYMam73-W3mwVPIrfGx6o-o4RbpysyHauhAU&s=C8gU_okaGYMsxtUoJSYuQ_vDn4BTbgW1GhoqPqnGHmI&e=>
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=J_gvdaMuoJPRuXHtCsbyYcmOlO4SHcnvdvV3yZsZP6U&s=-mVgZu0S5huxUVE7k3P90lFKq9OY-syNm7kxVygCaq4&e=>
--
Shawn Foor, SET

FOOR DESIGN, LLC
7640 E 77th CT
TULSA, OK 74133
P:918-237-1400
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to