That’s funny.  I believe that statement has been in the standard since before 
flex drops were even available.  

 



Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com

 

 
<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
 http://www.mfpdesign.com

 
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
 https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of bjnew...@aegisfirepro.com
Sent: Thursday, November 15, 2018 3:01 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: system modification hydro test

 

Yes.  We were told that the only instance where isolated drops that numbered 
greater than 20 would not require hydrostatic testing at 200 psi was if they 
were existing flex drops that were relocated within the original radius of the 
flex drop and they weren't removed from the existing system.

 

Their position was that, despite the commentary in the handbook, and the 
engineers opinions from NFPA's interpretations, the intent of this code is only 
referring to relocated flex drops.


 

B.J. Newlin
Service Sales

Aegis Fire Protection LLC
bjnew...@aegisfirepro.com <mailto:bjnew...@aegisfirepro.com> 
P (913) 825-0343
F (913) 322-4475
C (913) 238-0035

"Have the courage to say no. Have the courage to face the truth. Do the right 
thing because it is right..."

- W. Clement Stone

 

 

 

-------- Original Message --------
Subject: system modification hydro test
From: Matt Grise <m...@afpsprink.com <mailto:m...@afpsprink.com> >
Date: Thu, November 15, 2018 2:47 pm
To: "sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> "
<sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> >

We had a situation where a TI modification involved adding  over 20 mechanical 
t’s to a system (office area layout change). NFPA 13 2013ed 25.2.1.6 says 
“modifications that cannot be isolated, such as relocated drops, shall not 
require testing in excess of system working pressure”

 

The mechanical t’s could not be isolated, but since they were added heads and 
not “…such as relocated drops…” the AHJ required us to test the entire existing 
floor at 200psi.

 

Has anyone seen this before?

 

Matt 

 


  _____  


_______________________________________________
Sprinklerforum mailing list
 <mailto:Sprinklerforum@lists.firesprinkler.org> 
Sprinklerforum@lists.firesprinkler.org
 <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to