Yes
An AHJ can ask for anything.
We produce a letter outlining NFPA testing requirements  to the GC and dissolve 
us of any libilaty due to testing existing system and we dont test until they 
agree and sign.

Just SOP



Sent from my cell phone. Please excuse spelling etc.



Mark Phillips
Vice President of Fire Protection, Kirlin Carolinas, LLC
t: 919-526-1584 | m: 919-610-0490
[email protected] | https://kirlingroup.com
8000 Brownleigh Dr, Raleigh, NC 27617
-------- Original message --------
From: Matt Grise <[email protected]>
Date: 11/15/18 4:47 PM (GMT-05:00)
To: [email protected]
Subject: system modification hydro test

We had a situation where a TI modification involved adding  over 20 mechanical 
t’s to a system (office area layout change). NFPA 13 2013ed 25.2.1.6 says 
“modifications that cannot be isolated, such as relocated drops, shall not 
require testing in excess of system working pressure”

The mechanical t’s could not be isolated, but since they were added heads and 
not “…such as relocated drops…” the AHJ required us to test the entire existing 
floor at 200psi.

Has anyone seen this before?

Matt