They're calculated as an equivalent length, same size, same equivalent 
length, point him or her to table 23.4.3.1.1 (nfpa 13 2016)



Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]







From:   Rocci 3 Cetani <[email protected]>
To:     "[email protected]" 
<[email protected]>
Date:   03/05/2019 03:11 PM
Subject:        OS&Y "flow rates"
Sent by:        "Sprinklerforum" 
<[email protected]>



BE ADVISED - This email originated outside EMCOR. 

So we swapped out a broken OS&Y valve at the hospital and the OSHPD 
inspector is insisting he wants the “flow rates”  ( I assume he means 
friction loss) from the existing and new OS&Y valve. OS&Y valve cutsheets 
don’t have a friction loss chart because the loss is so minimal. Does 
anyone have any ideas on how to explain this to an OSHPD inspector, he 
have already told him this but he is just stuck on wanting to know the 
“flow rates” 
 
Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
 
Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590
 
 
[email protected]
www.norcalfire.com
 
CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information 
belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, 
or the employee or agent responsible to deliver this message to the 
intended recipient, you are hereby notified that any disclosure, copying 
or taking of any action in reliance on the contents of this information is 
strictly prohibited. If you have received this transmission in error, 
please immediately notify us by telephone to arrange for return of the 
documents.
 _______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=cuSgH-6rxCtyTAdlZ-YO7rIxY5qNKTQlmzGY2tnvfI0&s=SbcA0ul-X3ExiUNCsfb_c9T1jbaqzKgcSJi3uNOSMe0&e=




This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to