So, I’ve got an FPE and ME questioning about water hammer in a deluge system.

We have a unique installation where we have two levels of hose connections (one 
array at 12 ft AFF and one at 60 ft AFF) for manual firefighting in an 
unconditioned assembly building which is 145 ft high.

Due to the non-heated condition, one proposed concept for a semi-automatic 
system is to use an electric release deluge valve to charge the system from 
manual pull stations.

Flow rate will be 1,000 gpm at somewhere near 150ish psi though 600-800 ft of 
pipe inside the bldg.

The FPE and ME are concerned with water hammer in the piping when the deluge 
valve opens based on how fast the valve opens.

Has anyone dealt with or had to provide calcs for this?  NFPA 13, 14, etc. are 
fairly silent on the issue.  Is it even an issue?  I’ve never had this brought 
up before on an interior system.

Anyone have any data on how fast a solenoid operated deluge valve opens?

Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to