Looking for preliminary sizing for a water storage tank. Worst case for this 
particular building would be OH-2. (.2/1500 = 300gpm + 250 hose. 550gpm for a 
minimum of 60 minutes = 33,000 gallons). Per NFPA22 (2013) 5.1.3.1 round it up 
to 40,000 gallons. Does that sound about right?