Well I look at it this way.  If you used the curves and factored the value up 
by an additional 15 - 20% you should be fine considering the mantra is that 
most fires are controlled by only 1-3 sprinklers not the entire calculated 
hydraulically remote area.   But, if the committee believes it should be done a 
certain way then put it in black and white and eliminate any confusion and 
guessing.

Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>

From: Sprinklerforum <[email protected]> On Behalf 
Of Roland Huggins
Sent: Monday, March 25, 2019 2:03 PM
To: [email protected]
Subject: [EXTERNAL] Re: Water Tank

The NFPA 13 committee believes the tank size is indeed based on the CALCULATED 
volume of water.  I know this because I attempted several cycles ago to state 
we should simply use the curves with a modifier.  I was almost burned at the 
stake for uttering such blasphemy.

Roland


Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.
Dallas, TX
http://www.firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.firesprinkler.org_&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=LSitVO9kRtffCU2_Kq1AFwMHMwU4R9POZX1mHsm-XJo&s=ECrKtTShUpl6Us21CbW8dwSOVQYGFhIkaRkmw0MtKKQ&e=>

Fire Sprinklers Saves Lives




On Mar 20, 2019, at 7:48 AM, AKS-Gmail-IMAP 
<[email protected]<mailto:[email protected]>> wrote:

Tank sizing for some situations presents an uncomfortable dilemma because there 
are pressures from all sides to minimize the tank size yet we all know the tank 
contains the single most important item. Some codes can be argued to say the 
size is for sprinkler demand only. The code might also qualify that by implying 
the actual system calculated sprinkler demand is used for sizing. So in this 
case the OH-2 system might have a 1.8 overage at its most demanding location. 
But then what happens if the fire event occurs at the least pressure demanding 
part of the system where the overage is higher than 1.8? Here we can only hope 
that more water in less time is better and perhaps not so many sprinklers open 
and someone is present to manage the run time. The same pressures to limit the 
tank size might also work against installing a more water efficient sprinkler 
system for that OH-2 space.


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.