Not as a regular practice but we had an unusual residential project that was 
composed of 8 row homes that had to be separated by 11" because of something 
having to do either with property lines or seismic separation or both.  So 
instead of abunch of seismic loops, we ran a CPVC supply pipe down a walkway 
along one side of the building and did a service entry for each unit.

However one thing we do as a regular practice is when there is a satellite 
structure to a larger building, we take the connecting pipe underground (if 
there's no connecting structure overhead) and tie it to the larger building 
system.  Since Ames has just come out with small diameter in-building risers, 
it's a really clean solution to transition with those and pipe with CPVC.



Steve Leyton

(Sent from my phone; please excuse typos and voice text corruptions.)



-------- Original message --------
From: Skyler Bilbo <[email protected]>
Date: 3/22/19 2:33 PM (GMT-08:00)
To: [email protected]
Subject: Underground Sprinkler Lines

Has anyone installed CPVC piping for an entire fire sprinkler system 
underground?

We are being asked more and more on one story buildings to install wet systems 
where our mains are in the corridor and lines are in the walls.  This involves 
a whole lot of drilling of 2x4's and installing a bunch of protective nailer 
plates (a whole lot of man hours).

Seems to me like we could do it faster using a trencher, installing the vast 
majority of the piping underground with stub ups into the walls for sidewalls.  
I suppose in order to do this correctly, we would have to install a drain, 
perhaps by stubbing into a sump pit somewhere?

I know I have seen a small amount of CPVC piping installed underground in 
apartments that have open stairwells between units, and those don't have a way 
to drain the underground portion, even though this would be after the riser 
controls and fall under NFPA 13(R).

I'm really interested to know if anyone has done it, and/or if there are any 
big reasons not to.  To my knowledge, this isn't specifically addressed in our 
standards.