Blazemaster has a grooved CPVC adapter. Contact the Viking Rep and ask them 
what coupling is approved for that fitting.

Victaulic also has a line of grooved CPVC fittings but these don't appear to be 
for Sprinkler systems.

Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>

From: Sprinklerforum <[email protected]> On Behalf 
Of Dale Wingard
Sent: Thursday, April 04, 2019 12:25 PM
To: [email protected]
Subject: [EXTERNAL] RE: Grooved Coupling for CPVC

Try contacting your CPVC manufacturer and they should be able to provide you 
with a statement that the grooved adapter was made to be used with a standard 
coupling.

Dale F. Wingard, SET
Designer Commercial/Marine Division
NICET IV #76284
Water-based Systems

Hiller Systems
A Division of The Hiller Companies, Inc.

3751 Joy Springs Drive
Mobile, AL 36693
o: 251.661.1275
HillerFire.com

[Macintosh HD:Users:andrechiang:Dropbox:Emily's Files:Hiller:Email 
Signature:Hiller100 Email Signatures 2019-01-10:Hiller100 Email Signatures V1 
2019-01-10 - Systems.png]

Protecting life and property since 1919

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Mike Hairfield
Sent: Thursday, April 4, 2019 11:19 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Grooved Coupling for CPVC

Done that and I could not find anyone that has coupling that is approved for 
that use.

________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of [email protected]<mailto:[email protected]> 
<[email protected]<mailto:[email protected]>>
Sent: Thursday, April 4, 2019 12:17 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Grooved Coupling for CPVC


Check with your supplier or down load their grooved literature.



Regards,

G. Tim Stone



G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services



   117 Old Stage Rd. - Essex Jct., VT. 05452

CELL: (802) 373-0638   TEL: (802) 434-2968

             [email protected]<mailto:[email protected]>







From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Mike Hairfield
Sent: Thursday, April 4, 2019 12:11 PM
To: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Subject: Grooved Coupling for CPVC



I have a local AHJ asking for a data sheet that states that a standard grooved 
coupling is

U/L listed and/or FM approved for that use.



Have any of you guys ever seen this?



Thanks,



Mike

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to