My CPVC documentation states to user only flex couplings, not standard rigid. 

And I will give them one heart, and I will put a new spirit within you; and I 
will take the stony heart out of their flesh, and will give them an heart of 
flesh
Eze 11:19

> On Apr 4, 2019, at 11:24 AM, Dale Wingard <[email protected]> 
> wrote:
> 
> Try contacting your CPVC manufacturer and they should be able to provide you 
> with a statement that the grooved adapter was made to be used with a standard 
> coupling.
>  
> Dale F. Wingard, SET
> Designer Commercial/Marine Division
> NICET IV #76284
> Water-based Systems
>  
> Hiller Systems
> A Division of The Hiller Companies, Inc.
>  
> 3751 Joy Springs Drive
> Mobile, AL 36693
> o: 251.661.1275
> HillerFire.com
>  
> <image001.png>
>  
> Protecting life and property since 1919
>  
> From: Sprinklerforum <[email protected]> On 
> Behalf Of Mike Hairfield
> Sent: Thursday, April 4, 2019 11:19 AM
> To: [email protected]
> Subject: Re: Grooved Coupling for CPVC
>  
> Done that and I could not find anyone that has coupling that is approved for 
> that use.
>  
> From: Sprinklerforum <[email protected]> on 
> behalf of [email protected] <[email protected]>
> Sent: Thursday, April 4, 2019 12:17 PM
> To: [email protected]
> Subject: RE: Grooved Coupling for CPVC
>  
> Check with your supplier or down load their grooved literature.
>  
> Regards,
> G. Tim Stone
>  
> G. Tim Stone Consulting, LLC
> NICET Level III Engineering Technician
> Fire Protection Sprinkler Design
> and Consulting Services
>  
>    117 Old Stage Rd. - Essex Jct., VT. 05452
> CELL: (802) 373-0638   TEL: (802) 434-2968
>              [email protected]
>  
>  
>  
> From: Sprinklerforum <[email protected]> On 
> Behalf Of Mike Hairfield
> Sent: Thursday, April 4, 2019 12:11 PM
> To: Sprinklerforum <[email protected]>
> Subject: Grooved Coupling for CPVC
>  
> I have a local AHJ asking for a data sheet that states that a standard 
> grooved coupling is
> U/L listed and/or FM approved for that use.
>  
> Have any of you guys ever seen this?
>  
> Thanks,
>  
> Mike
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to