Look up the definition of compartment in the 2013 edition of 13R. It's
3.3.2 and defines a compartment as a space with four walls and a ceiling
(no floor required apparently). It goes on to say you can have openings to
an adjoining space if there's a minimum lintel depth of 8" and the total
width of openings in a single wall does not exceed 8'. It then goes on to
say the lintel is not required if there is a single opening of 36" width or
less hen there are no other openings to adjoining spaces. By that
definition it seems that your hallway and room are two compartments if the
entry from one to the other is 36" or less and there are no other openings
to any adjoining spaces. The only structures I can think of that meet that
criteria two room enclosures that have exterior entrances/exits and one
narrow opening between rooms. Since that doesn't sound right (why bother
with that nuance in the definition at all?) the Committee must have been
thinking of something else, some greater application.


Ron Greenman

[email protected]

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)


On Tue, Apr 9, 2019 at 1:24 PM Travis Mack, SET, CFPS, CWBSP, RME-G <
[email protected]> wrote:

> If I have a hallway with a 9’ ceiling and it opens into an area that goes
> up to a 12’ ceiling, would those be separate compartments?  The area with
> the 12’ ceiling is protected by a single sprinkler at 20’ spacing, and the
> hallway has 3 sprinklers at 16’ spacing.
>
>
>
> There is not a true lintel that projects down from the 9’ ceiling.
>
>
>
> [image: MFP_logo_F] <http://www.mfpdesign.com/>
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
>
> MFP Design, LLC
>
> 3356 E Vallejo Ct
>
> Gilbert, AZ 85298
>
> 480-505-9271
>
> fax: 866-430-6107
>
> [email protected]
>
> www.mfpdesign.com
>
>
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
>
> LinkedIn: https://www.linkedin.com/in/travismack
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
>
>
>
> *“**The bitterness of poor quality remains long after the sweetness of
> low price is forgotten.**”*
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to