Still I'd like to know what they mean by the second part of the clause that
allows omission of the lintel. Seems like this rule is specifically for
pyramids with the passageway from the outside opening into the burial
chamber.


Ron Greenman

[email protected]

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)


On Tue, Apr 9, 2019 at 2:43 PM Travis Mack, SET, CFPS, CWBSP, RME-G <
[email protected]> wrote:

> *Yeah.  I was getting lazy.  I went back and read definition after I sent
> that.  It is about a 10’ opening.  So, I just added the 4th sprinkler.  It
> didn’t really affect anything.  There was plenty of margin.*
>
>
>
> [image: MFP_logo_F] <http://www.mfpdesign.com/>
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
>
> MFP Design, LLC
>
> 3356 E Vallejo Ct
>
> Gilbert, AZ 85298
>
> 480-505-9271
>
> fax: 866-430-6107
>
> [email protected]
>
> www.mfpdesign.com
>
>
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
>
> LinkedIn: https://www.linkedin.com/in/travismack
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
>
>
>
> *“**The bitterness of poor quality remains long after the sweetness of
> low price is forgotten.**”*
>
>
>
>
>
> *From:* Sprinklerforum <[email protected]> *On
> Behalf Of *Ron Greenman
> *Sent:* Tuesday, April 9, 2019 2:41 PM
> *To:* [email protected]
> *Subject:* Re: 13R and compartment
>
>
>
> Look up the definition of compartment in the 2013 edition of 13R. It's
> 3.3.2 and defines a compartment as a space with four walls and a ceiling
> (no floor required apparently). It goes on to say you can have openings to
> an adjoining space if there's a minimum lintel depth of 8" and the total
> width of openings in a single wall does not exceed 8'. It then goes on to
> say the lintel is not required if there is a single opening of 36" width or
> less hen there are no other openings to adjoining spaces. By that
> definition it seems that your hallway and room are two compartments if the
> entry from one to the other is 36" or less and there are no other openings
> to any adjoining spaces. The only structures I can think of that meet that
> criteria two room enclosures that have exterior entrances/exits and one
> narrow opening between rooms. Since that doesn't sound right (why bother
> with that nuance in the definition at all?) the Committee must have been
> thinking of something else, some greater application.
>
>
>
>
>
> Ron Greenman
>
>
> [email protected]
>
> 253.576.9700
>
>
>
> The Universe is monstrously indifferent to the presence of man. -Werner
> Herzog, screenwriter, film director, author, actor and opera
> director (1942-)
>
>
>
>
>
> On Tue, Apr 9, 2019 at 1:24 PM Travis Mack, SET, CFPS, CWBSP, RME-G <
> [email protected]> wrote:
>
> If I have a hallway with a 9’ ceiling and it opens into an area that goes
> up to a 12’ ceiling, would those be separate compartments?  The area with
> the 12’ ceiling is protected by a single sprinkler at 20’ spacing, and the
> hallway has 3 sprinklers at 16’ spacing.
>
>
>
> There is not a true lintel that projects down from the 9’ ceiling.
>
>
>
> [image: MFP_logo_F] <http://www.mfpdesign.com/>
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
>
> MFP Design, LLC
>
> 3356 E Vallejo Ct
>
> Gilbert, AZ 85298
>
> 480-505-9271
>
> fax: 866-430-6107
>
> [email protected]
>
> www.mfpdesign.com
>
>
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
>
> LinkedIn: https://www.linkedin.com/in/travismack
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
>
>
>
> *“**The bitterness of poor quality remains long after the sweetness of
> low price is forgotten.”*
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to