We've had several project lately of noncombustible construction, all rooms
have ceilings except for a couple small janitor closets, and the walls of
the janitor closets don't extend up to roof deck - exactly as I interpret
JD's description.  We either got the GC to install ceilings in the janitor
closets, or we applied section 8.15.23.  The part about ". . .open to an
adjacent sprinklered space on only one side . ." doesn't make sense to me
either.  Right or wrong, I provided protection 24' in all directions that
didn't have a full height wall.  The only other alternative I see that 13
gives us is to sprinkler ALL the space above the ceilings, and that's way
overkill.  Protecting 24' beyond the walls of a 40 sf janitors closet seems
like overkill also, but I can justify that (to some extent) knowing I'm
protecting the steel roof structure from heat that could be rolling out the
janitors closet.  

 

Ed K

Bamford Fire

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Prahl, Craig/GVL
Sent: Tuesday, April 30, 2019 11:34 AM
To: [email protected]
Subject: RE: NFPA 13 8.15.23 Spaces above ceilings 2016 ed

 

I would consider that space a concealed space but the question is does that
space meet the criteria of 8.15.1.2.1?

 

8.15.1.2.1* Concealed spaces of noncombustible and limited combustible
construction with minimal combustible loading having no access shall not
require sprinkler protection.

 

Access is typically considered fixed (stairs or ladders) or readily
accessible for the use of storage.  If the space cannot be used for storage
it should qualify as not needing sprinklers per 8.15.1.2.1.  "No access"
doesn't necessarily mean the space has to be totally inaccessible.  Other
text within the Concealed section alludes to the access for storage use as
being one trigger for sprinklers.  If it meant absolutely no access then any
room with a lay-in ceiling would require sprinklers because all you have to
do is push up a tile to access the space.  

 

Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252 |
[email protected] <mailto:[email protected]>  |
<http://www.jacobs.com/> www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

 

From: Sprinklerforum <[email protected]
<mailto:[email protected]> > On Behalf Of JD
Gamble
Sent: Tuesday, April 30, 2019 12:22 PM
To: [email protected]
<mailto:[email protected]> ;
[email protected]
<mailto:[email protected]> 
Subject: [EXTERNAL] Re: NFPA 13 8.15.23 Spaces above ceilings 2016 ed

 

Craig, 

 

Would the space above the surrounding rooms (with ceilings) in your scenario
(which is exactly what I have) require sprinklers?  Are they even applicable
to 8.15.1.2 if they are not "concealed" areas?

 

 

 

Get Outlook for iOS
<https://urldefense.proofpoint.com/v2/url?u=https-3A__aka.ms_o0ukef&d=DwMF-g
&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoD
qOn85ooHi6vIkMag&m=eGsj2RKutL-U49x_bjC6r10FU48_Dh3j-PgVLl9Fwic&s=a7B8nb8rUh_
fyjame1c2WxVzC6b2vJV-EJpEw4bm84c&e=> 

 

  _____  

From: Sprinklerforum <[email protected]
<mailto:[email protected]> > on behalf of
Prahl, Craig/GVL <[email protected] <mailto:[email protected]> >
Sent: Tuesday, April 30, 2019 10:12 AM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: NFPA 13 8.15.23 Spaces above ceilings 2016 ed 

 

Word pictures are fun aren't they?   If the graphic doesn't show up, email
me and I'll email you directly.   The graphic is from 2016 ed of NFPA 13,
Figure A.8.15.23.3.

 

I'm going to use some random numbers to hopefully help clarify this in my
mind.

 

So, as an example let's say the rooms in the space including the IT room
have walls that extend up 10 ft.    The underside of the roof deck is 15 ft.
Rooms adjacent to the IT room have ceilings at 10 ft. but the IT room has no
ceiling and is open to the deck above.  So if I'm standing in the IT room I
can see into the open space above the ceiling in the adjacent rooms on all
four sides of the IT room.  Does that sound right?

 

If that is the case then let's walk through 8.15.23.

 

8.15.23.1:  Does the space above the adjacent ceilings require sprinkler
protection per 8.15.1.2?   If it meets 8.15.1.2.1 then, no.  So let's assume
that is the case.  No sprinklers. 

 

8.15.23.2 Spaces above ceilings are not sprinklered, so not applicable.

 

8.15.23.3  This is assuming you've provided sprinklers in the ceilings in
the adjacent rooms.  You'd extend the design area at the 0.6*Sq. Rt. of the
Design area or 24 ft 

beyond the limit of the IT room over the adjacent ceilings.    You would do
this on all four sides of the IT room as depicted in the graphic below.
Not sure why the writers of this section made the statement of this only
occurring on one side as this is not an uncommon occurrence having this
conditions on multiple sides of a room/space.  

 



 

 

 

Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252 |
[email protected] <mailto:[email protected]>  |
<http://www.jacobs.com/> www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

 

From: Sprinklerforum <[email protected]
<mailto:[email protected]> > On Behalf Of
Kyle.Montgomery
Sent: Tuesday, April 30, 2019 11:32 AM
To: [email protected]
<mailto:[email protected]> 
Cc: 'Cecil Bilbo' <[email protected]
<mailto:[email protected]> >; 'Pete Schwab' <[email protected]
<mailto:[email protected]> >
Subject: [EXTERNAL] RE: NFPA 13 8.15.23 Spaces above ceilings 2016ed

 

It's kind of a gray area, but I'm going to politely disagree with my friend
Travis and say that you can apply 8.15.23.3 and extend sprinkler coverage at
the deck only 0.6 times the design area past the room with no ceiling.

 

The trick is the wording. It's written as though the space with the ceiling
is the small space and the space without the ceiling is the large space. So,
if you had a small room with the ceiling that was an "island" in the middle
of a warehouse, for example, you could not apply this rule because it is
open to an adjacent sprinklered space on all sides. That's the opposite of
what you have.

 

You've got a situation where the space above the drop ceiling isn't open to
an adjacent sprinklered space on only one side, it's open to the adjacent
sprinklered space IN THE MIDDLE. Someone could make the argument that this
condition doesn't match the description so you can't apply it, and that
could be a strong argument. But I would say that if you look at the
intention of the rule, which is based on the fire not extending more than
half the design area into the area above the ceiling, I can't see a good
argument that says if you extend your coverage the minimum distance out from
your room that you haven't met the intention of the rule.

 

Fellows, please feel free to shoot some holes in my theory.

 

Kyle Montgomery

 

Aero Automatic Sprinkler Co.

21605 N. Central Ave.

Phoenix, AZ 85024

Direct: 623.580.7820

Cell: 602.763.4736

 <mailto:[email protected]> [email protected]

 

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of JD Gamble
Sent: Monday, April 29, 2019 5:39 PM
To: [email protected]
<mailto:[email protected]> ;
[email protected]
<mailto:[email protected]> 
Cc: 'Cecil Bilbo' <[email protected]
<mailto:[email protected]> >; 'Pete Schwab' <[email protected]
<mailto:[email protected]> >
Subject: [EXTERNAL] Re: NFPA 13 8.15.23 Spaces above ceilings 2016ed

 

Travis you are correct in your mental image of the room. We have three
locations that have come into question. One does only have one communicating
wall but the others have multiple. It's my impression as well that without
the full height walls, we have to add coverage. 

 

Get Outlook for iOS
<https://urldefense.proofpoint.com/v2/url?u=https-3A__aka.ms_o0ukef&d=DwMF-g
&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=eg
hgkfsX9abLYXeIrpwuoTYvdheDNXuDJORls3qcspo&s=2BqpXVsmVXyFyZ8Zb6f0fp_85JWt2YD4
y-aVWcmjmek&e=> 

 

  _____  

From: Sprinklerforum <[email protected]
<mailto:[email protected]> > on behalf of
Travis Mack, SET, CFPS, CWBSP, RME-G <[email protected]
<mailto:[email protected]> >
Sent: Monday, April 29, 2019 6:36 PM
To: [email protected]
<mailto:[email protected]> 
Cc: 'Cecil Bilbo'; 'Pete Schwab'
Subject: RE: NFPA 13 8.15.23 Spaces above ceilings 2016ed 

 

I'm not sure I get your total picture, but I'll try.

 

First, we start with sprinklers in all spaces.  Then we can ask if we can
omit in places.  The section you quote is only applicable if it is open on
one side, like figure A.15.23.3.  If your IT room is the space in question
and you have it open to rooms around it, then your don't meet the criteria
of open on only one side.  Based on very limited idea of what you have on
your project, I tend to think sprinklers would be required above the areas
adjacent to the IT room.  But I am envisioning the IT room as an island
surrounded by rooms on all sides, or at least more than one side.

 

 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com_&d=Dw
MF-g&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&
m=eghgkfsX9abLYXeIrpwuoTYvdheDNXuDJORls3qcspo&s=Hz3noah6lgQGs0WfbQ50ySTEV5UO
SJw9Co4ojCpIFOQ&e=> 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:[email protected]> [email protected]

www.mfpdesign.com
<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com&d=DwM
FAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecH
AoDqOn85ooHi6vIkMag&m=RT3tDDH1_OXBjwDVcUyvRKVl3dZVxrSHtDiNksc67_I&s=knyEy5SZ
uEvR42OG12hbLI5L91R8xwvRt3P90jTQsMQ&e=> 

 

Send large files to us via: https://www.hightail.com/u/MFPDesign 

LinkedIn: https://www.linkedin.com/in/travismack

 

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

 

 

From: Sprinklerforum <[email protected]
<mailto:[email protected]> > On Behalf Of JD
Gamble
Sent: Monday, April 29, 2019 5:31 PM
To: [email protected]
<mailto:[email protected]> 
Cc: 'Cecil Bilbo' <[email protected]
<mailto:[email protected]> >; Pete Schwab <[email protected]
<mailto:[email protected]> >
Subject: NFPA 13 8.15.23 Spaces above ceilings 2016ed

 

Can anyone explain how this section would NOT apply to the following
situation.

 

IT Room, open to deck, walls do not go full height.  Rooms around the IT
room are non/limited combustible above with hardlids below.  Currently no
sprinklers installed above the ceilings where spaces communicate with the IT
rooms open walls. (we are in the argument about it, State isn't much help).

 

Have I applied this section in error requiring sprinklers above the hardlids
because the walls are not full height based on 8.15.23?

 

JD Gamble

LSS of Sheridan Inc.

 

 

 

  _____  


NOTICE - This communication may contain confidential and privileged
information that is for the sole use of the intended recipient. Any viewing,
copying or distribution of, or reliance on this message by unintended
recipients is strictly prohibited. If you have received this message in
error, please notify us immediately by replying to the message and deleting
it from your computer. 

Jacobs' Energy, Chemicals and Resources business is now part of Worley

 

 

  _____  


NOTICE - This communication may contain confidential and privileged
information that is for the sole use of the intended recipient. Any viewing,
copying or distribution of, or reliance on this message by unintended
recipients is strictly prohibited. If you have received this message in
error, please notify us immediately by replying to the message and deleting
it from your computer. 

Jacobs' Energy, Chemicals and Resources business is now part of Worley

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to