I have two deluge systems fed from separate risers that have a large door opening between the two systems. Am I required to calculate both systems flowing.
[cid:[email protected]] NFPA 13 section 19.2.2 states that areas not separated by a partition shall extend 15 feet beyond the more demanding design area. So that means I have to flow both deluge systems at the same time, correct? Best, Timothy M. Easter