This is the standard arrangement on the Tyco Quell/Vanquish Sprinkler System
where we start the pump on the 1st stage detection on the Linear Heat
Detection. A Potter panel is used for control. We also have the pump
starting on drop in pressure as a backup.

Cheers.

Russell Gregory

Christchurch 

New Zealand

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Micah Davis, SET
Sent: Tuesday, 30 April 2019 9:27 PM
To: [email protected]
Subject: Prestart Pump - Preaction

 

Has anyone setup a pump on a preaction system to prestart at device signal
to get it prestarted before valve trip?  I have several large preaction
systems and am having issues with water delivery times.  I need to shave off
a few seconds and noticed that the program gives an option to have the pump
prestart.  We are required on this project to provide the water delivery
calculations, so I cannot use 7.2.3.4 to avoid the water delivery time
requirement.  

 

My specific question is, does anyone know of any concerns the contractor
should have for doing this?  Are there any operations/maintenance concerns?
Are false trips a problem?

 


Micah Davis, SET
NICET #124745
Water Based Systems Layout, Level IV 

Dynamic Fire Designs


 


Mail: [email protected]
Mobile: 931-242-1299
 <http://dynamicfiredesigns.com> www.dynamicfiredesigns.com 


Dynamic Fire Designs . 247 Winthrop Dr. . Spring Hill . FL . 34609

This message is confidential. It may also be privileged or otherwise
protected by work product immunity or other legal rules. If you have
received it by mistake, please let us know by e-mail reply and delete it
from your system; you may not copy this message or disclose its contents to
anyone. The integrity and security of this message cannot be guaranteed on
the Internet. 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to